Answer / kanupriya
ZCT is a neutral CT which is based on zero sequence current
detection. What happens during leakage, the current in the
phases are not the same & hence the in is not equal to
zero. This difference of current flows into the neutral CT
whicgh trips the RCCB
| Is This Answer Correct ? | 49 Yes | 15 No |
Answer / bhoot
ZCT is a neutral CT which is based on zero sequence current
detection. What happens during leakage, the current in the
phases are not the same & hence the in is not equal to
zero. This difference of current flows into the neutral CT
whicgh trips the RCC
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / shrikant muthineni
RCCB is the one which has both the propoerties of ELCB and
MCCB
| Is This Answer Correct ? | 25 Yes | 27 No |
Answer / g de nys
A ZCT is installed in the Neutral-Earth bonding conductor.
It will initiate a trip only when neutral current is
returned by the Protective Earth conductor rather than the
load neutral conductor. This usually occurs when there is
phase-earth leakage (or fault). This protection only works
effectively in Direct earthed installations (not MEN).
RCCB's operate by monitoring current balance with a CT
around all phases and neutral. A trip is initiated when
current flowing out one phase is not balanced by current
flowing in another phase (or neutral). This occurs when
current takes the return path via Protective Earth
bypassing the RCCB. This system works well in direct
earthed installations or MEN, provided the neutral is not
bonded to earth on the load side of the RCCB.
| Is This Answer Correct ? | 8 Yes | 12 No |
List the advantages of star-delta starter with induction motor?
Why transformer making sound during operations?
What is the function of automatic Transfer Switch(ATS) in details
how does high earth to neutral voltage affect electronic equipment?
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
how the percentage impedance affect the transformer loading when connected in parallel.?
What is the difference between Static and servo controlled voltage stablizer?
what is the purpose of checking IR and Megger values in motor windings?
What is the purpose of stand by earth fault protection for transformer ?
can anyone explain the star-delta motor control wiring ,which wire go where and how they operate?
What is a system?
what is formula for zero phase sequence of nuetal earthing transformer of 6.6 kv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)