How many earthing pits required for diesel generator set ? Why ?
Answers were Sorted based on User's Feedback
Answer / ankur bisen
For a single DG set, 4 earthpits will be required - 2 for
body & 2 for neutral. Suppose you have 3 DG sets then 8
earthpits will be required - 2 for body earthing of all
three DGs & 6 for neutral(2 for each DG). The two earthpits
for body shall be in grid. The two earthpits for neutral of
a DG shall also be in grid, but earthpits for neutral of
different DGs shall not be in grid.
| Is This Answer Correct ? | 95 Yes | 11 No |
Answer / s.madhavan
A DG set need 4 earth stations ( pits ) Two for neutral and two for body. They should be atleast 3 mtrs apart. two neutral station s are to be connected in grid and similarly two body earth station to be connected in grid.
When two are more Dg sets are running in parallel neutral pits of only one genset ( biggest ) are used. Neutral pits of other Dg sets are disconnected. The Body earths of all Dg sets will be as it is.
| Is This Answer Correct ? | 26 Yes | 7 No |
Answer / venkatesh
For a single DG set, 4 earthpits will be required - 2 for
body & 2 for neutral.Suppose you have 3 DG sets then 12
earthpits will be required - 6 for body earthing of all
three DGs (2 for each DG) & 6 for neutral (2 for each DG).
The two earthpits for body shall be in grid. The two
earthpits for neutral of a DG shall also be in grid, but
earthpits for neutral of different DGs shall not be in grid.
| Is This Answer Correct ? | 24 Yes | 13 No |
Answer / daljit
d.g set require two eartpit for d.g neutral and 2nd for
body earth.
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / sanjay kumar
According to Indian Std. DG Set Should have four Earthing
Pits Each Should have Separate Copper Plate Accoring to Std.
-Run two properly sized Copper or GI Earthing Conductors
from the Neutral Bushing/Terminal of the DG Set's
Alternator and connect one each to the two neutral earth
pits. Similarly, the alternator will have two earthing
terminal on its body (at diagonally opposite ends); Run two
properly sized Copper or GI Earthing Conductors from these
body earthing terminals of the DG Set's Alternator and
connect one each to the two body earth pits.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mistryhardik89
According to Indian Std. DG Set Should have four Earthing
Pits Each Should have Separate Copper Plate Accoring to Std.
-Run two properly sized Copper or GI Earthing Conductors
from the Neutral Bushing/Terminal of the DG Set's
Alternator and connect one each to the two neutral earth
pits. Similarly, the alternator will have two earthing
terminal on its body (at diagonally opposite ends); Run two
properly sized Copper or GI Earthing Conductors from these
body earthing terminals of the DG Set's Alternator and
connect one each to the two body earth pits. But, you MUST
inter-connect all these four (two neutral and the two body)
earth pits by properly sized Copper or GI Earthing
Conductor.
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / zexer
bcoz my mum didn't study engineering or related
how could she know newton (true? )
| Is This Answer Correct ? | 17 Yes | 23 No |
Answer / vishal
2, one for DG internal and another for DG body
| Is This Answer Correct ? | 16 Yes | 27 No |
Answer / balachandar
For higher rating of DG set, four earth bits are
required.Three earth bit is for Body earthing
(Engine,Alternator,acoustic) and one earth bit is for
neutral earthing.(I'm not sure)
| Is This Answer Correct ? | 16 Yes | 28 No |
Answer / s.gupta
FOR C.T. DIESEL GENERATOR , ITS 2 EARTH CONNECTION REQUIRED .
BCOZ OF ONE FOR DIRECT EARTHING PLANNING & THE OTHER ONE FOR
BODY CURRENT DISTRIBUTION.
BY, DR. S.GUPTA (M.TECH IN MECH. ENGG.)
| Is This Answer Correct ? | 4 Yes | 16 No |
How many btu per hour equals 1 ton of air conditioning?
what is the working principal of air compressor?
What will cause if you run your engine in critical RPM continuously?
Please send me IOCL-GET-Mechanical Sample Question paper/previous year paper or the Guidelines related to the same...i will be very thankful to you. i m going to apper for the written of the IOCL on 6th July,2008 Thank you
please send all previous solved question papers on HLL......
What are the things to do when approaching the port?
why piston is cylindrical in shape
7 Answers Clarion Technologies, Olam International,
What is raito of coolent level in DG
which is more harder ductile or brittle..????
• Do you consider yourself a leader?
1 Answers Petro Star Mount, Tech Mahindra,
Why not use dbt in cooling tower approach
id fan impeller vane direction &rotation direction
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)