how to use single phase supply for a three phase equipement.
Answers were Sorted based on User's Feedback
Answer / siddharth tayade
the diffrence between 3phase and single phase voltage is
only depends on the angular displacement . if we made the
anguler displacement 0deegre , 120deegre, 240deegre using
capacitor . then we can adopt the 3phase supply voltage.
Is This Answer Correct ? | 45 Yes | 0 No |
Answer / tufail
Take three connections from the single phase lie. Take one
as reference. Using capacitor-inductor combinations the
desired time lag (120,240 deg in time) can be obtained in
the remaining two.
Is This Answer Correct ? | 31 Yes | 1 No |
Answer / manish jain
By using a capacitor, an another phase with a 90 deg angle
difference can be introduced which can give a rotating
torque for a rotating three phase machines. So, in this
fashion a single phase supply can be used.
Is This Answer Correct ? | 30 Yes | 8 No |
Answer / mas
by using phase splitter ( having capacitorin series with
firing angle delayed as 12 ,240 ) we use 1 phse as three
phase
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sunny
with the help of ARNO CONVERTER we can use single phase
supply for a three phase equipment.
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / ashish
With The Help Of Phase Splitter We Can Provide the Three
Phase Supply From Single Phase Supply
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / nagoor meeran
with the help of capacitor bank we will spilit the phase angle and then connect the 3 phase equipement.......
Is This Answer Correct ? | 0 Yes | 6 No |
Answer / sanjay eliokem india
we can use vfd itwillconvert single phase to threephase
suply
Is This Answer Correct ? | 3 Yes | 14 No |
1) Can anyone give me a typical value for Insulation Resistance of 11kV xlpe cable? 2) How much will the IR value decrease per KM of cable length added?
In A.C systems, fuse is placed in phase-in order to disconnect the circuit during faulty condition. But, what is the reason for putting "LINK" in neutral istead of connecting through (same) wire.
what is interfacing in computer studies?
Please tell me the power flow from pmg to main rotor of an alternator (Including AVR unit)?
will we have to design the UPS differently for both i.e. if we want to connect the two batteries in parallel and/or we want to connect the two batteries in series ?
HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?
I want to know Electrical Circuit?
Why we are designed only 11Kv and 6.6Kv Alternators, not 33Kv Alternators and Power Transmission side we are designed only 220kv, 120kv, 66kv, 33kv, 11kv, and 440volts, not 20kv, 50kv, 100kv.
Compare salient pole and Hndrical rotor machines.
If the secondary winding will be open in current transformer, how to damage the insulators
why one side of tubelight glows after switch off ?
What are the causes of unbalanced current on 34.5kv feeder Ia=0.05,Ib= 0.25, Ic=0.15 and In=0.27 prior to tripping current are balance?