Answer / shailza
general occuring faults in motor are:
1. inst. overcurrent
I(1)the current is equal to 8.5 times the nominal current
rectification-isolate breaker, take megger and check motor
T.B
2. Earth Fault I(0)
rectification-take megger
3. Stalling I1(t)
rectification- take no load trial with decoupling of motor
4. Thermal overload Ith
rectification- check current balance
5.phase imbalance I(2) Check motor T.B and take megger.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kannan
1. Over load tripping - Reset OL relay.
2. Ball bearing failure - To be identify by heavy noice and
offton tripping & Over heat - Change bearing.
3.Monthly once clean the body of the motor. cooling will be
better.
4. Winding problem. - Check by megger of multi meter.
Rewinding to be done.
5. Over load relay itself problem some times.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pabs
Winding gets damage
If any Brake pad in motor also get damaged
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kokkiligadda venkata raju
over load trip
to control the ratings
under maintenance problem that means lubrications,cleaning
in this minimise to proper maintenance
remove the light damage parts in this cause to totally
motor damazed
it' minimise to replace the parts
over temperature
it's minimise to fix the fans to rotor
| Is This Answer Correct ? | 0 Yes | 0 No |
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
what is the type of motor that is used in emu units in india
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
I want to apply for ONGC recruitment 2012 .I am BE Electrical but it is mentioned that to apply for this post you have to have Electrical supervisor certificate .so please tell me from where can i get such certificate ???
Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million
what curve and rateing would you use for a three phase 0.75kw motor?
what is mean by restructuring power system?
What is the different types of cable & current capacity of cable
role of shunt coil in circuit breakers
How to calculate current carrying capacity of copper conductor _ such as cable size 25sq mm,50 sq mm, 75 sq mm, 100 sq mm
electrical knowelge
why and where we use early make & late break contacts in protection?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)