Answer / shailza
general occuring faults in motor are:
1. inst. overcurrent
I(1)the current is equal to 8.5 times the nominal current
rectification-isolate breaker, take megger and check motor
T.B
2. Earth Fault I(0)
rectification-take megger
3. Stalling I1(t)
rectification- take no load trial with decoupling of motor
4. Thermal overload Ith
rectification- check current balance
5.phase imbalance I(2) Check motor T.B and take megger.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kannan
1. Over load tripping - Reset OL relay.
2. Ball bearing failure - To be identify by heavy noice and
offton tripping & Over heat - Change bearing.
3.Monthly once clean the body of the motor. cooling will be
better.
4. Winding problem. - Check by megger of multi meter.
Rewinding to be done.
5. Over load relay itself problem some times.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pabs
Winding gets damage
If any Brake pad in motor also get damaged
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kokkiligadda venkata raju
over load trip
to control the ratings
under maintenance problem that means lubrications,cleaning
in this minimise to proper maintenance
remove the light damage parts in this cause to totally
motor damazed
it' minimise to replace the parts
over temperature
it's minimise to fix the fans to rotor
Is This Answer Correct ? | 0 Yes | 0 No |
Why the ratation of fan is anticlockwise all over the world?
What is IDMT? What is the principle
how we can improve power factor from 0.8 to 0.85 or 0.9 & how we identify its either lag or lead ? thank you
I am using submission of two ct in one and half scheme for 67/67N protection. Both CTs star point is grounded separately near ct box.Will two point ground give wrong tripping to 67/67N during fault or no matter.
why the LED of my electrical meter glows even after the line has gone. what actually the reason?
how to calculate the no. of turns in secondary side of CT?
What are the parts in a inverter?
why we are using star connection and delta connection? difference?
why we use 50hz frequency in india why not other frequencies like 52,59,42 etc
Why used IGBT IN AC Drives
1.what is the difference between MPCB and MCB ? 2.what is the difference between MPCB and MCCB ?
what types of fault occurred in transmission line ? which protection function senses the fault?