general occuring faults in motor are:
1. inst. overcurrent
I(1)the current is equal to 8.5 times the nominal current
rectification-isolate breaker, take megger and check motor
T.B
2. Earth Fault I(0)
rectification-take megger
3. Stalling I1(t)
rectification- take no load trial with decoupling of motor
4. Thermal overload Ith
rectification- check current balance
5.phase imbalance I(2) Check motor T.B and take megger.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kannan
1. Over load tripping - Reset OL relay.
2. Ball bearing failure - To be identify by heavy noice and
offton tripping & Over heat - Change bearing.
3.Monthly once clean the body of the motor. cooling will be
better.
4. Winding problem. - Check by megger of multi meter.
Rewinding to be done.
5. Over load relay itself problem some times.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pabs
Winding gets damage
If any Brake pad in motor also get damaged
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kokkiligadda venkata raju
over load trip
to control the ratings
under maintenance problem that means lubrications,cleaning
in this minimise to proper maintenance
remove the light damage parts in this cause to totally
motor damazed
it' minimise to replace the parts
over temperature
it's minimise to fix the fans to rotor
| Is This Answer Correct ? | 0 Yes | 0 No |
why fuse amperes rating are specified ratings like 32amp & 64 amps?
What is the diffrence between ofline ups and online ups?
What is AVR in Turbo generator in Thermal power plant?
what is the concept of star delta starter?
can we use only a isolator in the subtation..
Explain about 3 phase motor fault current calculation with examples?
what is meant by poly phase induction motor ? how its operating by single phase or three phase?
difference between circuit breaker and switchgear?
what is the difference between 'Control Transformer & Potential/Voltage Transformer'?
what is the maximum load sutiable from earth to phase and what is the max voltage earth to phase suitable
i have installed my solar site of 6.7kw and is working perfectly , can somebody tell me that how can i measure my solar irradiation kw/day/sq m ?
Why the cost of CT increases with the decreasing of its CT Ratio (Technical Reason)?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)