Do you know the faults occurs generally in motors and how
to rectify them?
Answers were Sorted based on User's Feedback
Answer / shailza
general occuring faults in motor are:
1. inst. overcurrent
I(1)the current is equal to 8.5 times the nominal current
rectification-isolate breaker, take megger and check motor
T.B
2. Earth Fault I(0)
rectification-take megger
3. Stalling I1(t)
rectification- take no load trial with decoupling of motor
4. Thermal overload Ith
rectification- check current balance
5.phase imbalance I(2) Check motor T.B and take megger.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kannan
1. Over load tripping - Reset OL relay.
2. Ball bearing failure - To be identify by heavy noice and
offton tripping & Over heat - Change bearing.
3.Monthly once clean the body of the motor. cooling will be
better.
4. Winding problem. - Check by megger of multi meter.
Rewinding to be done.
5. Over load relay itself problem some times.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pabs
Winding gets damage
If any Brake pad in motor also get damaged
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kokkiligadda venkata raju
over load trip
to control the ratings
under maintenance problem that means lubrications,cleaning
in this minimise to proper maintenance
remove the light damage parts in this cause to totally
motor damazed
it' minimise to replace the parts
over temperature
it's minimise to fix the fans to rotor
| Is This Answer Correct ? | 0 Yes | 0 No |
In order that work may be done:(a) Two wires are necessary(b) The circuit must have a switch(c) Coal must be burnt(d) A supply of energy is required
sir please send me previous year questions of jspl through which i could prepare myself fpr the test.
64 Answers FGH, HFT, Jindal, Jindal Steel and Power, JSP, JSW, Lin Engineering,
Why transformer neutral earthing? What is advantages?
Whatis the current capacity of 33KV/ 0.433KV transformer on Primary and secondary side/
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
star delta connection used in reduce the starting current at 3 times . how its reduce the current please explian .
Can we inject more current in ct primary paralleling 2 loading transformers/Injection kit at a time?let ct ratio be (5000/1A)(per kit rating 2000A range),i need to inject 5000A,if this cant b done means wat is d optional?
working principle of UPS
Why the Petrol Guns in the Petrol bunk are earthed?
How to control motor gearbox speed and friquency? If length of cable and dia given, how to measure the voltage drop?
why the voltage is in digit of 11/33/132/220/440 please send me on shukrerabbi_abkhalil@rediffmail.com with thanks
Why is it that variation allowed in supply voltage to motors is (+ or -)10 %, whereas that in frequency is (+ or - )5 %
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)