Answer / mugil
Instrument Earth:
Instrument Earth is also called as Reference earth.Instrument Earth all individual shields(Screen) and
over all shields single or multi pair cable shall be isolated from electrical earthing due to avoiding interference and terminated different bus bar.
Instrument bus bar will be connected to grounding dispatcher by 25 sqmm green- yellow cable.Grounding dispatcher to earth pit is connected to 70 sqmm green -yellow cable.
Electrical Earth:
Electrical earthing also called as dirty earth or protective earth.It is used to protect the power system,electrical equipment and personnel from electric shock.
| Is This Answer Correct ? | 17 Yes | 3 No |
Dear Shashank,
There are mainly three types of earthing used in instrumentation.
1) Power earth
2) Signal / Instrument Earth
3) IS Earth
Power earth :
Provides ground reference to all power cables. Usual practice to have MAX . Earthing resistance ~ 100 Ohms (There is no harm if it is lower)
Signal / Instrument Earth :
Provides ground reference to all Signal cables (including ICS systems).
Usual practice to have MAX . Earthing resistance ~ 10 Ohms (There is no harm if it is lower)
3) IS Earth (Intrinsically Safe Earth) :
Provide ground reference for all IS signals. MUST NOT EXCEED 1 OHM.
You can have multiple earthing pits of same kind of earth and can be connected in parallel in order to reduce the over all resistance.
| Is This Answer Correct ? | 13 Yes | 9 No |
Answer / elam
How long distance need to plant earth to instrument earth
| Is This Answer Correct ? | 4 Yes | 1 No |
Wht should be the ratio of natural frequency (Fn) to wake frequency (Fw) and wht if goes above the rato limit?
We are used ABB 800xa 5.1.please tell me how to instrall this.
what is the difference between Ethernet unmanaged and managed Switch?
A pressure Tx accuracy is 0.2%. Signal o/p is 4-20ma.span is 16 Ma.how many deviate the o/p then calibration needed
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
My flow transmitter range is 0-1000mmwc.DCS range is 0- 100m3/hr.What is correspond out put in terms of milliamps if my flow is 65m3/hr
what is the meaing of calibration curve?
can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0 to 10 Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we will feed to the PLC.
can any one help me to get bel probational engineers sample question papers. I have applied for it.
WHY WE R NOT USING THE TURBINE FLOW METER IN THE STREAM SERVICE ? pl explain?
What are primary elements of measuring pressure?
admittance level sensor meaning?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)