Answer / jafar
for calculating cable size first we have to calculate load current
example 1 : 3KW POWER (1phase)
current i= 3*1000 /(230*0.8)
= 16.3A
for current carrying capacity of 1 sq mm copper is 2.4A
for current carrying capacity of 1 sq mm AL is 1.4A
now here if we use Cu then cable size is 16.3/2.4
= 6.79 is our calculated value
so we can choose near size of cable which is 10 sq mm
example 2 : 100W power (3 phase)
current i= 100*1000/(1.732*400*0.8)
= 180A
like that above
cable size is 180/2.4 = 75
so near size is 95 mm2
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / love kumar
for three phase copper cable is consider as 1sq mm ,3amp.
for aluminium cable 1sqmm -1amp
| Is This Answer Correct ? | 0 Yes | 0 No |
I have a 25 KVar capacitor bank at my facility.How to check the capacitor bank ??
what r the types of detectors? state the location these detectors?
what is phase and neutral.
what is meant by generator differencial protection?
what is meaning of bus raiser???
why the value of k is more in shell typr transformers?
Sir, plz tell me how droop setting is done in parellel operation od DG set ? please give practical example ?
Define de-sensitivity?
What is infinite Busbar?
what is cutoff voltage?
How many earthings are required for commissioning the Transformer?
In explosive and polluted environments which type of motors do we use?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)