How i can calculate the cable size for given load,there is any formula,for 3 phase and single phase
Answers were Sorted based on User's Feedback
Answer / jafar
for calculating cable size first we have to calculate load current
example 1 : 3KW POWER (1phase)
current i= 3*1000 /(230*0.8)
= 16.3A
for current carrying capacity of 1 sq mm copper is 2.4A
for current carrying capacity of 1 sq mm AL is 1.4A
now here if we use Cu then cable size is 16.3/2.4
= 6.79 is our calculated value
so we can choose near size of cable which is 10 sq mm
example 2 : 100W power (3 phase)
current i= 100*1000/(1.732*400*0.8)
= 180A
like that above
cable size is 180/2.4 = 75
so near size is 95 mm2
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / love kumar
for three phase copper cable is consider as 1sq mm ,3amp.
for aluminium cable 1sqmm -1amp
Is This Answer Correct ? | 0 Yes | 0 No |
is there any device that works properly accept relay, it may be fuse but if i want fuse of 33kv 300 amp it is avaliable, pls give me details
Consider three heater bank connected in 3 phase star with neutral.Each heater bank connected in each phase.So each phase get 230 volts supply.my question is,during balance condition, current flow in neutral or Not
which transfofrmer oil break down voltage strength get will be more if oil sample taken from bottom of tank or oil sample taken from top of the transfomer tank.
wath is skin effect?
If one lamp connect between two phases it will glow or not?
Please tell me if you are electrical engineer,and you are appointed for the maintainance of Electrical Power plant,then which parts of the plant deal with you.Also tell how these parts/components work.
What's the part of OTCC in transformer?
In single core cable, Why non-magnetic material is used??
need of capacitor used in plant
Starting times for soft starter & power factor is thier any standard or datas available in manufactures list. Kindly suggest.
What is the basic difference between AVR and stabilizer?
2 Answers Gujarat Alkalies and Chemicals GACL,
1.Why we use choke?If we use for high starting voltage then different type choke gives different voltage. Is it correct?