what is neutral grounding resistor?
Answers were Sorted based on User's Feedback
Answer / himadri de
Neutral Grounding Resistor (NGR) is simple resistance connected in series between the neutral point of transformer and Earthing pit/point of neutral conductor.
NGR reduce the problems such as insulation breakdown caused by transient over voltage produce by arcing ground fault in underground system and damage to motors and switch gear caused by arcing in solidly grounded system.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / r.sateesh kumar
Neutral is nothing but return path ground that is called neutral .
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / r.sateesh kumar
Netrual is nothing but return path to ground that is called neutral
Is This Answer Correct ? | 0 Yes | 2 No |
Bimetal strip used in overload relay what is that,which types of material used for that & percentage.
What is open loop and control loop systems?
want happens when a dc is given to a commutator
how circuit breaker work.. what is the operations taking place inside a circuit breaker when an overcurrent occurs... is it similar to fuse?
what s the differenc between electrical &electronis , how to define them
what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?
how to calculate the current carrying capacity of cable
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
What is pole of the system?
Hi, I've just got into my electrical engineering course and I need some help with a question of mine here. During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz. From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
What iz main protection of mediuum voltage motors and what iz the standard IR voltage of 6.6 and 11kv motors.
3 phase supply is there Total kw 100 howmuch cable put the load