if we use contactor & MCCB both in a feeder.in this feeder
rating of contactor is higher or lower or same of MCCB
rating & why?
Answer / k.prakashchandra
It is of no use if the settings of both is the same.The one
nearest to load should have a lower setting.
| Is This Answer Correct ? | 0 Yes | 1 No |
What's difference between a400amps lt contactor and a400amps lt circuit breaker
how to calculate full load current of transformer & induction moter ?
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor frequency at maximum torque point is A 3.33% B 4.44% C 5.55% D 6.66%
what rectifiers is and what are the types of rectifiers?
How to calculate the current rating of power cables ?
CAN WE CALCULATE THE NEGATIVE SEQUENCE AND ZERO SEQUENCE REACTANCE OF A GENERATOR USING ONLY ITS RATED VOLTAGE, KW, PF AND SYNCHRONOUS REACTANCE??? IF YES, THEN HOW??
what is meant by auto transformer?
what is skin effect
what will be the neutral to earth voltage while checking by the Digital multimete? and why?
what is fuction static switch in ups and tell me use parts name and fucion
Why we Do not connect the windings of the motor in delta? & what would happen if we do that? I mean the winding themselves not the three lines that are coming to the motor?
what is lrs tank water resistance.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)