Answer / abdul

It depends on the how much the power factor has to be improved
simple calculation would be
Kvar = KW [tan (cos inverse (old pf) - tan (cos inverse (new required pf)

Is This Answer Correct ?    5 Yes 0 No

How the value of KVAR of capacitor bank used in switchgears calculated??..

Answer / girish

KVAR=KWX0.541(Power factor improvement at 0.98)

KW=20
KVAR=20X0.541

10KVAR

2.5KVAR 4 Steps

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the meaning of TRF

1 Answers   Khidmah,


It is desired to flood light the front of a building 42 meters wide and 16 meters hig.Projectors of 30 degree beam spread and 1000 watt lamps giving 20 lumen/watt are availabl.If the desired level of illumination is 75 lumen/m and show a suitable scheme.Assume the cofficient of utilization, deprecitation factor and waste light factor are 0.4, 13 and 1.2 respectively.

0 Answers  


in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv, it operate or not???

4 Answers   Divis Laboratories,


why neutral and body earthing of transformers kept separated? what is distance between two is required as per is?

6 Answers  


Why we specify TNC switch with 1NO 1NC ,2NO 2NC ? how we get connection.?

0 Answers  






hi this is hema can anyone mail me previous years questions for the APPSC-A.E.E (in electrical stream.) ......thank u.

0 Answers  


what is the formula of knowing the clabe size on any load?

1 Answers   JSW, Scan Steel,


What do you mean by the zone of protection?

0 Answers  


why farmers are use earthing instead of neutral for their light conec. at field.is it safe

2 Answers   Honeywell,


1.why should we connect the measuring instruments in l.v side in short circuit test of a transformer? 2.why the power factor is less in open circuit test of a transformer?

0 Answers  


What should be the dielectric strenght value of transformer oil of 11/0.433KV distribution transformer and 33/11KV tranmission transformer ?

2 Answers  


why the value of k is more in shell typr transformers?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)