How the value of KVAR of capacitor bank used in switchgears calculated??
Answers were Sorted based on User's Feedback
Answer / abdul
It depends on the how much the power factor has to be improved
simple calculation would be
Kvar = KW [tan (cos inverse (old pf) - tan (cos inverse (new required pf)
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / girish
KVAR=KWX0.541(Power factor improvement at 0.98)
KW=20
KVAR=20X0.541
10KVAR
2.5KVAR 4 Steps
| Is This Answer Correct ? | 0 Yes | 1 No |
What is the role of link in neutral in a three phase ac system?
How do you select a cable size(cu&Al)for a particular load?
how to calculate energy meter multipling factor by ct & pt raitio
What is the difference between lubricating oil and insulating Oil?
what are all the components required to assemble solar panel other than pv cell?
Why the substation measure in KV but not in the power ratings of transformer.
what is the path of thunderlightening? once both a buffalo and a person were standing 5m apart but lightening hit and killed buffalo not person?
1.how many types of relays? 2.difference between ATS& STS?
Weather power factor correction needed for synchronous motors?
TO CALCULATE THE RESISTANCE OF GRR OF HT MOTOR 400KW WHEREAS STATOR VOLTAGE 6.6KV AND ROTOR VOLTAGE 705V AND ROTOR CURRENT IS 346A.
what is the difference between control transformer and Potential transformer (PT)?
how to calculate the distance relay faulty zone?pls explain?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)