Explain REF protection and sbef protection in transformer?
Answer Posted / k.prakashchandra
REF is restricted earth fault relay, for internal earth fault of Tr . SBEF is standby earth fault relay or backup for both internal and outside earth faults . The CTs of both are connected to neutral of Tr. Discriminative setting is required
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What are the different methodes for calculating the short circuit Current?
What are motor generator sets and explain the different ways the motor generator set can be used ?
Role of active and reactive Power sharing in between two synchronized Generators, Droop Setting role ?
What is Diff btw Fire Alarm & VESDA System???
What is meant by earthhing of a magnetic flow meter and when to use empty pipe detection?
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
working function importance of mdc meter
in electrical control panel. how can i choose the cable rating. (example - 11kw motor, 18-25A mpcb}
what is thermal resistance of PVC Cable.
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
What are the advantages of speed control using thyristor?
Draw the single line diagram of the power station?
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box