Answer / vinod
NGR capacity should allow the mininmum earth fault current
so that system with minimum earth fault current can be
detected and isolated by earthfault relay.
ie NGR fuction is to reduce the earth fault to the minimum
level in the range of earth fault relay
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / raghavendran.r
As far I know the formula is Rngr = Vln/Ig.
where Ig is the current flowing through the Neutral Grounding resistor(let through fault current), which depends upon the type of system you haver chosen, i.e High impedance grounding or Low resistance earthing.
The let through ground fault current through the neutral is low for High resistance earthing and its High for low resistance earthing.
But the important condition is that the let through fault current should be greater than the system capacitive charging current to avoid transient over voltage.
| Is This Answer Correct ? | 2 Yes | 1 No |
when we switch on the switch and load is not connected at home,is electricity wasted?
What is referred to the electron in the outer orbit?
details of oil cell size of Breakdown voltage test of tranformer oil details as per Standardswith mushroom electrodes?
Am using an electronic digital display to see the RPM of ABB ACS 550 drive, which is showing negative value when the motor & drive in stop mode but it is showing correct value during the run mode. can anyone help me out??
2 Answers Bala Power Solutions,
Why one can experience electrical Shock due to Voltage or Current?? or both voltage or current??
arcing is due to only capacitance or it is due to both inductance and capacitance? explanation.
phase association of 3PH L&T static CT meter is wrong. means 1PH & 1 CT connected properly and other 2 voltage and CT's inter changed. what would be the impact in the reading?
how "rabbit ACSR" conductors are more efficient than "weasel ACSR" conductors
Can you use step up generator transformer of voltage ratio 16.5kv/420kv in place of step up generator transformer 15.75kv / 420 kv
How to calculate the cable size in sq. mm. when the load is given in KW?
- two pumps must work with them at the same time but if the first pump start the second pump must delayed for some time to start also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it
what is reluctance?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)