how to calculate the ngr capacity(nutral grounding resistor) ..

Answer / vinod

NGR capacity should allow the mininmum earth fault current
so that system with minimum earth fault current can be
detected and isolated by earthfault relay.
ie NGR fuction is to reduce the earth fault to the minimum
level in the range of earth fault relay

Is This Answer Correct ?    7 Yes 0 No

how to calculate the ngr capacity(nutral grounding resistor) ..

Answer / raghavendran.r

As far I know the formula is Rngr = Vln/Ig.

where Ig is the current flowing through the Neutral Grounding resistor(let through fault current), which depends upon the type of system you haver chosen, i.e High impedance grounding or Low resistance earthing.

The let through ground fault current through the neutral is low for High resistance earthing and its High for low resistance earthing.

But the important condition is that the let through fault current should be greater than the system capacitive charging current to avoid transient over voltage.

Is This Answer Correct ?    2 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

why steady state stability limit is greater than transient stability limit ? How it can be explained ?

0 Answers  


wht is this amps in power consuption and how can we convert that into consuption hours ? i am a sales executive of a energy saving lamps .

5 Answers   KSEB,


Where can I get Iidian straderd specifications for electrical items or works in web? please help me.

0 Answers  


why we used dc supply for field in dg set

0 Answers   Hindusthan National Glass,


which VFD is better ( LT or HT)

0 Answers  






BRIEFELY EXPLAIN MEGGAR PRINCIPLE

2 Answers  


what is the diff.between neutral and earth?

4 Answers  


how to reduce the transformer size in ups ?

2 Answers  


Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.

1 Answers  


after parallaing two generators current is shooting up in both the generators.for ex: load is 400 kw..after paralling and load sharing current in running gen is approx 900 amps and incoming is 750 amps which is too high when trying toshift the load current in incoming gen is coming more than 1300 amps and both getting tripped and making blackout..

3 Answers  


1.wat is the purpose (or)function of regulator? 2.wat is the purpose of stabiliser?

3 Answers  


What is a copper loss or i2r loss pc?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)