how to calculate the ngr capacity(nutral grounding resistor)
Answers were Sorted based on User's Feedback
Answer / vinod
NGR capacity should allow the mininmum earth fault current
so that system with minimum earth fault current can be
detected and isolated by earthfault relay.
ie NGR fuction is to reduce the earth fault to the minimum
level in the range of earth fault relay
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / raghavendran.r
As far I know the formula is Rngr = Vln/Ig.
where Ig is the current flowing through the Neutral Grounding resistor(let through fault current), which depends upon the type of system you haver chosen, i.e High impedance grounding or Low resistance earthing.
The let through ground fault current through the neutral is low for High resistance earthing and its High for low resistance earthing.
But the important condition is that the let through fault current should be greater than the system capacitive charging current to avoid transient over voltage.
| Is This Answer Correct ? | 2 Yes | 1 No |
Whatis the procedure for getting Electrical (light) licence while Iam a diploma holder in electrical Engg . I Compleated my one yr Apprentice training & worked as a junior engineer (ele) for 2 yr(contract basis).
in star-delta tranformer,if the input of star connection is 400/7v 3 kva then what is the output of delta connection?
Will a 230VAC motor run OK at 208VAC.
In 1000KVA Transformer why does we connect HT with delta connection and LT with star connection.Illustrate by showing formula?
How to calculate the time setting for star connection in star delta starter? For example 10KW 3PH Induction motor.
0 Answers Taj Group, Tata Steel Limited,
why we use choke in tubelights nad other lighting fixer
diff between grounding & earthing
8 Answers BARC, Mobiserv, NTPC, Tata Steel Limited,
how can i get an electrical c-certificate?
What is LOTO?
State four criteria's for selection of site for nuclear power station.
110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
What is the formula for finding fault level of generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)