15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ?
and what will be per phase current for 15 kva
Answers were Sorted based on User's Feedback
Answer / h s sandhu
In case of 15 KVA single phase dg set ,the current shall be 37amp while in case of 3 phase 15 KVA the current shall be 22Amp . It is a simle case of formula used for power P=VXI
Is This Answer Correct ? | 0 Yes | 0 No |
What is the function of NGR for the parallel operation of alternator? whats happen when different rating of alternator are running with parallel?
why transformer capacity is called KVA and motor capacity is called HP/KW? Why transformer capacity cant call HP/KVA?
How many size of cable required for a 300m long and 30kw inductive lode
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
Why armour HT XLPE power cable required to Earth?
can volts/Hz be relied upon to use 460v,60Hz electric motors on a 380v,50Hz power supply?
what is the type of starter used in tube light?
what happens when you connect a.c and d.c supplies
A transformer has negative voltage regulation when its load PF is A zero B unity C lagging D leading
When we are working on transformer(132\11KV). we are going to isolate the transformer from both HV side and LV side. then we are applying grounding on both side. My question is that we required to isolate the VT which is still connected from secondary side.?
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
what is acceptance test in electrical engineering.