why do we use LPF wattmeter not UPF in the experiment of no load and blocked rotor test of 3phase slipring induction motor?
Answers were Sorted based on User's Feedback
Answer / pritish
in case of no load test, the supply voltage is rated but the current drawn by the induction motor is very less; no load current, which produces only the core loss of the stator and some mechanical loss. in no load condition, the angle between V and I are high as a factor the pf will be less. hence to calculate the pf accurately LPF wattmeter is used. during loaded condition current increases and angle decreases hence pf increases.
any more clarification regarding this should be sent to pritish.nath@gmail.com
Is This Answer Correct ? | 36 Yes | 3 No |
Answer / saurabh wani
We use LPF only for no load test because at no load only reactive component of current flows in any machine. In 3 phase induction motor magnitude of reactive component current is more because of air gap. So power factor under no load operation is low and we use LPF wattmeter . If we use here UPF then it will give reading at time of starting only and after 3to 4 sec pointer will stable at zero no deflection.
Is This Answer Correct ? | 3 Yes | 1 No |
is the power of a single phase induction motor(Fans) is constant under varying speeds?
What is the ratio of Booster transformer?
what is through fault?
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
How to calculate incomer of a capacitor bank/feeder from its KVAR, AND how to calculate the copper busbar for rated incomer,like for 400A we calculate the 40x10 of aluminum busbar.
directional relay is typically used to respond in fault condition who it can be used just as reverse power protection which purely senes direction reversal to operate a circuit breaker?
why the admittance matrix or y bus matrix of a large network is called sparse matrix?
what is real , reactive and apparani power
A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram
Name different types of fault and which instrument is used to measures earth,short,open cicuit fault?
6 Answers NTPC, Vijai Electricals,
how to convert psi into kilo pascal? what is the suction pressure & discharge pressure of chiller?
how much mininmum length required to conduct a DC Hipot Test on 33kV AC Cable with 45kV DC? Is it 20meter or Less then 20?