during parallel operation of two ac generator which
condition must match before taking both parallel i.e
speed /voltage rating /kva/exciation
Answers were Sorted based on User's Feedback
Answer / pswin
Parallel operation of alternators is called synchronization. A synchroscope is an instrument for indicating the correct time for switching on. Three conditions must be fulfilled for synchronization.
1. Voltage must be same.
2.frequency must be same. And
3.voltage should be in phase position with respect to local series circuit.
Additional requirement is that the phase rotation must be the same.
Is This Answer Correct ? | 27 Yes | 3 No |
Answer / kamlesh g patel
incoming machine voltage should match the system/other
generator voltage.
frequency must be the same.
phase sequence must be the same.
Is This Answer Correct ? | 12 Yes | 4 No |
can I connect 25KvA stepdown transformer(RYB-440V,UVW-240V) to the output of 15KvA,3-phase online UPS(440V phase to phase)please brief.
What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??
As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why?
What safety followup during kWh meter isolation
how actually an anti pumping device works? what is the operational principal?
Can we convert off load tap changer transformer to on load tap changer transformer
when elecromagnatic waves are propogated in a wave guide?
HOW TO DESIGN THE body EARTH cable(Copper Conductor) size for 60KVA UPS?
For small size, high frequency coils, the most common core material is- a. )Air b. )Ferrite c.) Powdered ion d.) Steel
IF I USED VVVF DRIVE IN FAN APPLICATION MOTOR IN 6.6 KV ( 700 KW) MOTOR & DURING NORMAL RUN OPERATION TIME IF RPM SUDDENLY REDUCE IN MOTOR BY DRIVE(E. MOTOR RPM REDUCE SUDENLY 687 TO 550 RPM) WAHT WILL BE HAPPEND IN DRIVE
I have current, kva How can calculate kv?
What is the difference between earthed & unearthed system?