How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
If the load is 100 A ,the meter records correctly if the CT ratio is 100/5 as the meter gets 5A current . If the CT ratio is 600/5 the current in the meter will be 5/6 A for the same load current . Hence to get the correct reading ,multiply by 6.
| Is This Answer Correct ? | 8 Yes | 2 No |
WHY STABILIZER SHOULD USED
assume we are put both df/dt and vector surge relay in same bus the df/dt relay setting is +5 hz an -5HZ. we want operat the vector surge relay before the df/dt how i calculate the setting of the vector surge relay.
why D.C excitation is given to sunchronous motor?
What is voltage ratio of a transformer?
Waht will happened if reactive power increase in the line? waht about active power increase too?
EXPLAIN THE WORKING OF SERIES REACTOR IN HT CAPACITOR BANKS (FOR VOLTAGES & CURRENTS)
why starter use to on a motor
What is corona ? Mention its positve effects .
how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263 Amp ?????????
What is a diode?
through which medium return supply given to alternator please answer in details
why the starting torque is high in dc series motor..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)