How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
If the load is 100 A ,the meter records correctly if the CT ratio is 100/5 as the meter gets 5A current . If the CT ratio is 600/5 the current in the meter will be 5/6 A for the same load current . Hence to get the correct reading ,multiply by 6.
Is This Answer Correct ? | 8 Yes | 2 No |
pls give proper discription of selection of transformer based on particular load.
Define relative stability.
what type of euse we should use ? 1- High resistance & low temperature 2- High temperature low resistance
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
in power generator normaly voltagr betwween esth to neutral is 0 but my work place generator show the volatge is 60v any body know why? thanks
What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing?
Where the Dry type tranformers are used.
How should i design a 1ph & 3 ph transformer. Kindly let meknow all steps and formulaes related to design from scratch.
What is thef ormula to calculate the rating of a capacitor for a single phase motor
How check proper electrical earthing of machine.
How to reduce power factor correction capacitors failure in an industrial environment with vsd and computers usage in the system
why we are using auto transformer in sub station mostly???