How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
If the load is 100 A ,the meter records correctly if the CT ratio is 100/5 as the meter gets 5A current . If the CT ratio is 600/5 the current in the meter will be 5/6 A for the same load current . Hence to get the correct reading ,multiply by 6.
| Is This Answer Correct ? | 8 Yes | 2 No |
what is difference b/t ac current and dc current
4 Answers L&T, Meghana Engineers,
Define unilateral circuit?
why an ideal voltage source has low internal resistance????
5MVA TRANSFORMER SUDDENLY FAIL WITH THE PRV TRIPPING AND LARGE AMOUNT OF OIL SPREAD OUT? SO IT CAME BACK WITH THE REPAIRING WITH REASON THAT IT FAILS BCOZ OF TRANSIENT EFFECT? SO PLZ EXPLAIN HOW DOES IT HAPPENED?
How do we find the rating of a transformer, if it got burnt badly.
Why transformer used in UPS??
What is the purpose of reactor in over head transmission line.Can you any explain it.
2 Answers Dr Reddys, L&T, Reddy Labs,
HOW TO CALCULATE BATTERY BACKUP TIME & AH CAPACITY AGAINST UPS KVA RATING?
sir, in a industry present pf is 0.54 pf 25hp power is there its want improve 0.9 pf. which suitable capacity capacitor is suitable please inform me.
without any excitation we can strt any dc or ac moter?
what is the diff between earth leakage relay and earth fault relay?
how to test an MCB
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)