sir, in a industry present pf is 0.54 pf 25hp power is there
its want improve 0.9 pf. which suitable capacity capacitor is suitable please inform me.
Answers were Sorted based on User's Feedback
Answer / vishwas g. darne
You can use the the degree of P. F. Correction your load is
25 h.p. i.e. 25*746=18650-18.65kW present p.f.is .54 require p.f. is 0.9 degree of p.f. is 1.075 required kVAR per kW is 1.075 Therefore capacitor rating should be 1.075*18.65=20.04kVAR.
| Is This Answer Correct ? | 2 Yes | 1 No |
What will happen if we parallel two transformer with different %impedace?
What is the output of 25 kva 11/.4 kv transformer in kw ? Plz generalized it...
How to Calculate Contracted Maximum demand using motor Hp or Current
Either It Possible a dc Motor to Run On Ac Drive [ Ex : ACS 800 , Yaskawa F7 ] If it is Possible How Pls Inform Me dinesh_elect_eng@yahoo.com
When we getting shock, its we getting from voltage or Current.
The MCB circuit breaker have a voltage rating of 440VAC it's possible to supply a voltage of 480Vac
please give me all the Alarm .Trip ,Safety Relays & Conditions of UPS Systems mail me on ashokbabunhce@gmail.com
difference between brush less & brush excitation in a generator?
can we use the step down transformer to step up transformer
block diagram of 2 ups system connected in hot stand by mode?
im electrical engineer, could any one help me for FEWA exam questions please ?
should Dy11 and Dy1 group can be operated in parallel??????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)