sir, in a industry present pf is 0.54 pf 25hp power is there
its want improve 0.9 pf. which suitable capacity capacitor is suitable please inform me.
Answers were Sorted based on User's Feedback
Answer / vishwas g. darne
You can use the the degree of P. F. Correction your load is
25 h.p. i.e. 25*746=18650-18.65kW present p.f.is .54 require p.f. is 0.9 degree of p.f. is 1.075 required kVAR per kW is 1.075 Therefore capacitor rating should be 1.075*18.65=20.04kVAR.
| Is This Answer Correct ? | 2 Yes | 1 No |
how to calculate the lightning arrester conductor @ no of earth pits required
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
Why 60Hz frequency is used in America what are all the benifits?
What are your future plans for the company if permanently employed?
What is the technical name of Transformer Oil ?
17 Answers Bhel, Don Bosco, Lanco,
What meant by XLPE cable
what is difference between VAT & CST
What is Primary and Secondary Injection Test of CT and Relay.
What does quality factor depend on in resonance?
what is rating boiler
I need the proper answer on :- What is the Earthing Value as per the standard for Raw power and UPS Pit and in panel /DB N-E value ???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)