we want to feed 3 phase supply to 70 ton AC load.what will be the size of (3 phase)cable require.
Answers were Sorted based on User's Feedback
Answer / faizan
For cable selection we need supply voltage,load current and distence between source to load end ,then we can choose the size of cable and also it depends on meterial of cable,( cu/alu )..
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pratap
70 ton=245280watt
I=245280/1.73x440x.8
=402 Amp
cable size 400sq.mm(3 phase +neutral)
| Is This Answer Correct ? | 2 Yes | 4 No |
1. What does mean of "PS" stand for Diff. CT class? 2. What is the formula of KW for 1Phase load inturms of voltag,current & P.F.?
How to calculate the breaker's short circuit current?
what is formula of illumation calculation
What is the differance between negative dc voltage and positive dc voltage because some circuit uses -24,-5,-12,- 15,volt dc supply
10 Answers eLab, Hero Honda, NTPC, Suzlon, Teradyne,
what is the operation of regulator in fan?
How to connect the earthing in aircraft?
What is DG B-check and C-Check
What is meant by derating factor?
what is the UPS
Explain bypass capacitor?
why distribution transformer are of DY11 type?
Can We Apply DC POWER To Transformer???? And Why????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)