two 100W/230V bulb are connected in series. what would be
the voltage drop across 1 bulb
Answers were Sorted based on User's Feedback
Answer / sharath kumar
its the half of the voltage what we supply .. because the two bulbs have same ratings
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / vishwa theja c
(115v )half of the supply voltage across each bulb and power
consumed by each bulb will be reduced to 1/4 ae power is
proportional to square of voltage (25w).
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / dineshdamam
Applying kirchoff's voltage
law
we get the eqn
V= I*R1 + I*R2
now since both the lamps
are identical hence we get
V= 2I*R
230= 2I*R or
I*R = 115 =voltage drop
across each lamp.
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / muhammad shoaib
in series voltage drop is not same so across one bulb
voltage drop is 230v/2=150v
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / ramkrishna
p=100w
v=200
i=?
i=w/v
i=100/230=0.434
r=v/i
230/0.434=529.953917
voltage drop at 100w v=ir
v=0.434*529.953917=230v
Is This Answer Correct ? | 8 Yes | 15 No |
What is the full form of GSL wire
how would you determin the horsepower of a motor without a nameplate
how many types of accuracy class in ct? what is meaning of 5p20?
What about Reactive power.and role of that one?
No load test of induction motor is carried out to compute= A stator resistance B rotor resistance C magnetizing reactance D rotor reactance
why when i start my diesel generator it takes 1 minute or less then stop, and i checked the oil sensor is ok and when the generator start i can get 220 voltage but it it is stop after 1 minute or less, how can i solve this problem?
if we give connection of 100watts bulb through a single phase energy meter ,the disc of a meter rotates why it happens?
How Kneepoint voltage of CT practically related when CT in service. ie Knp is above 670 what exactly means
WHWT IS USE OF VACCUM CIRCUIT BREAKER
I have 800 Amps MG Fix type breaker It is in on line & it has been given only UV (under voltage)coil connection for tripping purpose.now it is not working properly means its getting tripp so how can i replace it or how can i rectify the problem without destrubing my load??????????
How phase displacement change in the over current relay coils.
A 400KVA ,50HZ TRANSFORMER IS TO BE OPERATED AT 50HZ.THEN KVA RATING OF THE TRANSFORMER?.