how to calibrate TT transmitter
Answers were Sorted based on User's Feedback
Disconnect the field sensor.
Connect a calibrated/traceable temperature signal calibrator.
Apply LRV value.
Trim the 4.0mA output.
Apply the URV value.
Trim the 20.0mA output.
Check as many interim points as the calibration protocol requires and note the output and the deviation from the expected value.
Determine whether the transmitter is within spec from the deviation values seen.
If transmitter passes, reconnect the field sensor to the input.
Fill in the paperwork.
Carl Ellis
Measure First
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / eid elatawy
First i have to know the connected element
1. RTD :using resistance box and divide the range into 4 quarters for example the range 0 to 100 deg we have 0,25,50,75,100 will find the related resistance from the table and see the transmitter output and if any deviation will make trim zero and span trim.
2. TC the same idea but we use MV supply and by using TC tables.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / karishma
First do span and zero adjustment of a temperature transmitter. Then when the input signal is zero the output is 4mA if not readjust the span and zero again provide 25% 50% 75% 100% Signal and see the output it should give 20 mA for 100% signal input.
| Is This Answer Correct ? | 1 Yes | 0 No |
What does a hookup diagram look like? can you give sample drawing. thanks.
In dcs panel we are using diff type of modules ?what is module ? what is the use of modules ?diff type of module?
If we increase only P what will be controller action ?
What is the DIfferences between SMART transmitters and PROFIBUS DP/PA Transmitters?
What is the difference between HMI and SCADA?
How to convert 4 wire level transmitter connection to 2 wire.
What's the Installtion procedure of DP Transmitter for Gas,steam and water?
What is DeltaV?
what is the difference between plc & DCS?
5 Answers Cheminova, NGIL, Siemens,
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
How u measure the massflow in orifice flow measurement techniques
How to calibration a control valve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)