For 7.5kw star delta starter how to calculate
1. Mccb rating
2. Contactor rating
3. Over load relay rating
Answer / joeredd
You need to know the full load motor current at the supply voltage you are going to be using. Your contactors/overload are rated on current. Their voltage rating needs to be higher than the supply voltage. (I.e. 415vac supply, 600vac rating). Knowing the motor wattage (7.5Kw) on its own is not helpful.
Is This Answer Correct ? | 3 Yes | 0 No |
What is expand formation of AYFY cable
What are the components connected in between the power supply coming from an electric pole to HT & LT Panels in a large commercial building or how the power supply connected from Electric pole to Transformer & then to the HT & LT panels of a building? Please send me answers via mail, my id is yogiagarwal@gmail.com. If possible, please give a line diagram.