Answer / rajesh
During faults (short-circuits), fault currents have two
components- AC component (Periodic) and DC Component
(Aperiodic). DC component will be decayed as per system X/R
ratio. circuit breakers are manufactured and tested to
break the fault current of specific AC component (Ib) and
DC component(Idc). Together can be called as Asymmetrical
breaking current.
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / vasu
DC component in circuit breaker is not related with trip
circuit system, it is related with making or breaking the
circuit at fault condition.
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / prathees
In a circuit breaker, always the trip circuit is DC. And it
is powerd by some battery back-ups or ups.
Because, even is the total power to the substation is gone
by some problems or faults, the trip circuit can be
operated without any problem as it is the safety for all.
| Is This Answer Correct ? | 14 Yes | 12 No |
Answer / ramesh.k
In circuit breakers having trip and close coils are purely
dc components, some CB's are having antipumping coils also
pure dc components and spring charge motor used as both ac
and dc.
| Is This Answer Correct ? | 19 Yes | 18 No |
In CB basicaly on HVCB DC ckt is used for their protection
ckt (making/breakin) and indication ckt as well as for
auxilary ckt like antipumping/hunting ,PD,
| Is This Answer Correct ? | 1 Yes | 9 No |
Answer / murugavel
dc closing coil,spring chargingmotor,tripping coil, andi
pumpingcontactor
| Is This Answer Correct ? | 0 Yes | 8 No |
Answer / amit mathur
The closing coil and the tripping coil with dc to dc
convertor for appropriate operation.
| Is This Answer Correct ? | 0 Yes | 8 No |
Answer / arunmozhi
circuit breaker in closing coil and tripping coil worked
for DC voltage.spring charge only used for 220v AC voltage.
| Is This Answer Correct ? | 1 Yes | 11 No |
Answer / sunita
in circuit bkr. only closeing and triping coil is a DC
component spring chargeing motor is generally AC motor
| Is This Answer Correct ? | 10 Yes | 32 No |
what is the safety of voltage power transformer(2250KVA0
in a large three phase induction motors usually the value of full load slip is
HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR CIRCUIT BREAKER?
Multimeter show phase to neutral volt 230 the per phase but phase to phase 415 not show 460 why.
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
how calculate gd2 of ht motors
4 Answers Hindustan Copper Limited, Kohler India,
we use 400/5A ct and 35/roor3KV,/0.1/root3KV,0.1/root3KV pt ratio. What is the multiple factor of this meter.
why the all high voltage transformers are in 11kv , 33kv , 66kv, 132kv like that
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
how steam converted into electricity in power plant
which is the best book of electrical objective for placement
Installation method of self treated earth electrode.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)