if our load in 3 phase circuit is 4000 amp. calculate the capacity of capacitor panel if line power factor is.80 .
Answer / aditya karkar
182.25kvar capacity of capacitor needed.
solution= IL:4000A V:440V COS@1=.8
SO FIND REAL POWER P.
THEN PUT IT IN Qnet=P(tan@1-tan@2)
we have to make pf 1.so take @2=0
| Is This Answer Correct ? | 3 Yes | 2 No |
what is impedance?
what is the maximum current carrying capacity of a 95 sqmm cupper under ground cable laid partialy in land and partialy in ground?
what is transient voltage?
During FEED, you will have all the information with regards to cable. How will you calculate the MTO for MV and LV Cables? what are your considerations?
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
What is LSIG ?
-What is leakage current . how much leakage current is allowed.
what is the benift of HT metering & LT metering
what is the meaning of the symbol << >> put in transformer drawing
A charge of 240 C is transferred in 2 minutes. The current flowing is:(a) 480A(b) 120A(c) 2A(d) 8A
difference between local breaker backup relay or backup protection relay ?
can anyone pls expain me about how can we design a cable tray??suppose if have to draw a 3 nos of 50 sqmm AYFY and 2 nos of 35 SQmm of AYFY cable through the tray..how can we design the tray size?? regards...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)