if our load in 3 phase circuit is 4000 amp. calculate the capacity of capacitor panel if line power factor is.80 .
Answer / aditya karkar
182.25kvar capacity of capacitor needed.
solution= IL:4000A V:440V COS@1=.8
SO FIND REAL POWER P.
THEN PUT IT IN Qnet=P(tan@1-tan@2)
we have to make pf 1.so take @2=0
| Is This Answer Correct ? | 3 Yes | 2 No |
why ac signals are sinosuidal
How to set a Zone 1 distance relay for distribution feeder?
0 Answers Schweitzer Engineering,
How much is the starting current for HPMV lamps. How many lamps can u wire in a circuit
How can we decide the fualt levels of sub-stations?
2 Answers Bhel, Enercon, Prakash Industries,
how much battery need for 2kv online ups for 2hr backup
why transformer measures in kva
what are the tests comes under the type test, what tests comes under routine tests.
plz tell me in my que,how to connect thw electrical wirening in house?
what is earth fault relay 64T, why it is used in main Incomer and neutral CT of Transformer.
What do you understand by avr?
How we can determine short circuiting current any plant and for example a plant which power generation is 415 volts and plant load is 500 kw.
What is the basic difference between 90% stator earth fault and 100% stator earth fault, and its phenmenona?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)