Answer / pawanchauhan12
basically this type of problem created when motor winding delta coil sequence not proper. For finding of fault following this processor :- Firstly check motor winding continuity 1:5{RR} ,2:6{YY} & 4:3{BB} .if continuity not matched then interchanged sequence of {RR} wire of power .if problem not solved then again interchanged second sequence of {YY} wire of cable .
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / pramit dutta
By connecting the stator winding 1st in star and then in delta
,the line current drawn by motor at starting is reduced to 1/3 th as compared to starting current with the windings connected in delta.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / santosh kumar kishore
in delta connection motor takes more current and in star
position motor takes less current so either change
connection or increase relay setting.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / a p patil
motor star connection join winding terminal C2,A2
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naveen joshi
There are many reason whether resistance increased by terminal contact in motor or phase difference in roter and stator not matched during transition from star to delta , increase the pause timing in timer .
.
| Is This Answer Correct ? | 0 Yes | 0 No |
One amps in HT is equal to how manys amps in LT
what is purpose of using reactor in substations.
20 Answers Heavy Engineering Corporation Ltd HECL,
why we are called the 4-20ma transducer,not 0-20 ma transducer??
What is the formula to calculate capacitor bank rating for a certain load.
what is the constructional difference between a power transformer and potentian transformer?
whats the diff b/w mpcb and mcb?weather it trips on single phasing or not.
9 Answers Electra Power, Essar,
What core magnetic balance test of transformer? How to do this test in a three phase Star delta (star-LV, Delta-HV) transformer? How to measure and where to measure? thanks and regards Austin
22 Answers Neutech, Power Grid, TSSPDCL,
what is the difference between neutral and earth
1 sq.mm alluminum cable hou much current caraing capacity
In the N-series schneider reclosers. What is the difference between current during fault time and current at tripping? This appears in the Event log in an event of a trip out.
What is turbocharger in a generator?
For these 2 devices what their power ratings are ? 1) single phase : AC 220V & starting amps 3Amps (i.e. starting torque) and the stabilized amps 2A ... For deep freezer 2) single phase : AC 220V & starting amps 2.7Amps (i.e. including the starting torque of a CRT monitor) and the stabilized amps 1 Amps thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)