Rtd sensor how to calibrate
Answers were Sorted based on User's Feedback
Answer / ahmallam
RTD Sensor can't be calibrate , you can only calibrate the transmitter only by potentiometer according to PT100, PT1000, ...... table.
or you can use comparison calibration.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / carl_ellis
An RTD is 'calibrated' by heating or cooling it to various
temperatures, measuring its resistance at those
temperatures, and the recording and analyzing the measurment
results.
An RTD's performance can not be adjusted like a temperature
transmitter's output can be adjusted, but its performance
can indeed be measured in a periodic calibration.
Carl Ellis
Measure First
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ajay kumar gupta
An RTD is 'calibrated' with the help of Temp. bath by selecting required temprature. You can compare RTD resistance, RTD Chart accordind to type RTD. There is no adjustment in RTD.
Before installation RTD in field this checking is must.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / yugesh shah
Calibration of rtd is not possible , yeah just know about error is possible when other rtd same type using in same place ..
Is This Answer Correct ? | 0 Yes | 0 No |
what does ip65 signify??what is its NEMA equivalent???
CAN WE CALIBRATE LEVEL TRANSMITTER USING HART COMMUNICATOR WHEN WATER LEVEL IS PRESENT IN THE BOILER SHELL?
can any one explain in which term we are flow flow is it volumetric r is it mass? and y
what are the steps to follow force a particular input or out put from ics triplex esd system?
what is orfics working in main steam line. is it increase pressure, velocity of steam flow and dicrease steam flow rate. or any other
what is difference between HOT permit and cold permit
in the boiler in the main steam line and its bypass line and the startup vent vales are only motorised valves why cant we use other types of valves such as pneumatic.
How can we calibrate pressure and flow transmitter in the field(online)?
Why we are using temperature and pressure as a reference when measuring flow of steam?
why micro controller 8051/52's clock frequency is internally divide by 12 ?? and why it is further divide by 32 in UART serial communication ??
what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?
Dear Sir/Madam, I am attending an interview for ETs in BHEL. I have cleared my written test under Electronics (Instrumentation). This is the first time I am appearing for an interview. Can any one who has attended the interview earlier give me a clue to face the interview. With regards Sindhu