I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
Answer / carl_ellis
A closed pressure vessel requires a differential pressure
measurement in order to compensate for the pressure or
vacuum in the vapor space above the liquid.
The density is said to be 1, so we'll assume that what was
really meant is that the specific gravity is 1.00, the same
as the specific gravity of water. The measurement can be
made in engineering units of mm of water column (wc) with no
compensation for a specific gravity other than water.
A DP transmitter measurement:
(high side pressure) minus (low side pressure)
The low side pressure reading is (vacuum pressure).
The high side pressure reading is (column of water pressure
+ vacuum pressure)
(water column pressure + vacuum pressure) minus vacuum
pressure = water column pressure.
With a vertical elevation difference between the flanges of
440mm, the water column pressure will be
0 - 440mm wc.
LRV = 0.0 mm wc
URV = 440 mm wc
Carl Ellis
Measure First
Is This Answer Correct ? | 5 Yes | 0 No |
what is a device net.
how to control pid
Need Intergraph softwares like SPI(INTOOLS),sp3d,PV ELITE, SP P&ID. CONTACT : logu.2211@gmail.com (8867825756)
what is input and output cards of plc needs to be hot swappable mean
What is rtd output signal
what are the sensor types of vibration&speed?n what is proximity sensor?
what is the difference b/w normal thermocouple and skin type thermocouple?
Please explain the difference between instrument range and calibration range in terms of pressure transmitter? line design pressure: 93 bar operating pressure : 82 bar press Transmitter Range? calibration range ?
What is NODE in DCS?
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?
For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
What is electronics?