I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1



I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's ..

Answer / carl_ellis

A closed pressure vessel requires a differential pressure
measurement in order to compensate for the pressure or
vacuum in the vapor space above the liquid.

The density is said to be 1, so we'll assume that what was
really meant is that the specific gravity is 1.00, the same
as the specific gravity of water. The measurement can be
made in engineering units of mm of water column (wc) with no
compensation for a specific gravity other than water.

A DP transmitter measurement:
(high side pressure) minus (low side pressure)

The low side pressure reading is (vacuum pressure).
The high side pressure reading is (column of water pressure
+ vacuum pressure)

(water column pressure + vacuum pressure) minus vacuum
pressure = water column pressure.

With a vertical elevation difference between the flanges of
440mm, the water column pressure will be
0 - 440mm wc.
LRV = 0.0 mm wc
URV = 440 mm wc

Carl Ellis
Measure First

Is This Answer Correct ?    5 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is a device net.

1 Answers  


how to control pid

0 Answers  


Need Intergraph softwares like SPI(INTOOLS),sp3d,PV ELITE, SP P&ID. CONTACT : logu.2211@gmail.com (8867825756)

0 Answers   GE,


what is input and output cards of plc needs to be hot swappable mean

1 Answers  


What is rtd output signal

4 Answers   Nestle,






what are the sensor types of vibration&speed?n what is proximity sensor?

3 Answers  


what is the difference b/w normal thermocouple and skin type thermocouple?

1 Answers   Heisco,


Please explain the difference between instrument range and calibration range in terms of pressure transmitter? line design pressure: 93 bar operating pressure : 82 bar press Transmitter Range? calibration range ?

3 Answers   L&T,


What is NODE in DCS?

2 Answers  


If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?

2 Answers  


For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?

2 Answers   NA,


What is electronics?

6 Answers   ITC Infotech,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)