Answer / nitin patil
i am giving here the formula for the same,
temp/ pressure = (ma - 4)* span / 16
where, ma = what you measured by multimeter
span = max range of the transmitter.
| Is This Answer Correct ? | 51 Yes | 6 No |
Answer / arun raja.s
Eg. you want to convert in DCS mean it for pressure
transmitter
field pressure Range : 0-100 Bar
Transmitter Calibration Range : 0-100 Bar so output 4-20
mA Depent on the Transmitter input pressure.
This output cable goto Analog input module, in DCS have
to set 0-100 Bar it work depent on 4-20 mA input.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mastersensor80
the sensor in the transmitter sense the physical effect
(pressure/level/flow) in the transducer this effect is
converted to electrical effect where we can measure 4 -20
ma for example that on the transeducer and the sensor
part,but to answer the above question it is mainly as
answered by Nitin Patil it is merly calculation as the
forumla provided by Nitin.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / neeraj pundir
with the help of transducer we convert (temp,pressure) in
outputs milliamps signals.
| Is This Answer Correct ? | 5 Yes | 3 No |
Milliamps output can be converted to temperature or
pressure, by means of converting the amps to volt by placing
a 250ohm resister across the circuit.
| Is This Answer Correct ? | 11 Yes | 18 No |
what is the input to be given digital temp controller during the the calibration time?
Describe the basis on which alarms should be generated and how their associated priority is determined
What is the difference between PLC and DDC?
What are the uses of orifice plates?
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
why can't we use 5-20mA standard or some other instead of 4- 20mA?
Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?
What is Cryogenic?
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
I want measure the volumetric flow of gas in waste heat recovery Boiler?Tell me how and which type of instruments required. Plz mail me:naba02222@gmail.com Sam please post the answer .
how many types of thermocouple cable are? give the name of each type.
What is difference between scada and virtual instrumentation?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)