Dear Friends,
Need your help for connecting APFC panel,
Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR)
Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
Answers were Sorted based on User's Feedback
Answer / moh
Please use a bus-coupler circuit breaker between the circuit breaker of TR1 and the circuit breaker TR2 with interlock (mechanical or electrical). When one TR is out the another TR will connect to another load and APFC by the bus -coupler circuit breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / moh
Please use bus -coupler circuit breaker between the o/p of the circuit breaker TR1 and the o/p of the circuit breaker of TR2 with mechanical and electrical interlock between the circuit breakers.When one TR gone out the another TR will connect to another load and APFC by the bus-coupler circuit breaker. good luck
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / qamar abbas
you may switch on capacitors manually from APFC 2 to control the power factor. if you have the same bus bar connected to both transformers
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srinivasvemana
Dearsir
you placed one ct tr -1 incoming ct connection given in Apfc-2 and apfc-2 power also take from tr-1.after you have 2 apfc panels working on one transformer.
| Is This Answer Correct ? | 1 Yes | 2 No |
by what factor the starting current is used when comparing star and delta connection for motor starting?
How out of step protection relay works?
how to select DG set for certain load?
How to calculate capacitor bank size at a load 800kVA.
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
What difference between TRANSFORMERS and TRANSDUCERS???
Explain the advantages and disadvantages of thermal power plant?
what happen to a dc series motor if it given as ac supply accidentaly
Dears we deal in Chemical are Plate earthing. Kindly call if any requirement and questions. Tech Earth Solutions Mohit Verma 8791071007
How to apply 'c' license and also explain what is difference between 'c' and 'b'license.i am also working in one of the private company.i have finished my diploma in 2014 .i have already finished in ITI electrician course.....
what will happen if the bus PT fuses are accidently removed from the circuit in 6.6kV feeder?
what is the difference between KW and KVA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)