what is the generator rating for 40 amp load of 3phase motor.??
400v voltage of generator...
plz tell me with formula its urgent...plzzz...
and also tell me that this 40 amp at all phases mean 40 amp
on red,40 amp on yellow,40 amp on blue......
or the total sum of that 3phase is 40 amp....
Answers were Sorted based on User's Feedback
Answer / king
P=root3*VI cos¡è.
this is the formulae for your question?
where
root3=1.732
V =APPLIED VOLTAGE
I =FULL LOAD OF THE
MOTOR
cos¡è=0.85
P= rating of generator
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / moitrita roy
2nd ans is the total sum of that 3phase is 40 amp.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / awaisranazai
thnxx king :)
plz also answer my this question.....u answerd me one
question...other is
and also tell me that this 40 amp at all phases mean 40 amp
on red,40 amp on yellow,40 amp on blue......
or the total sum of that 3phase is 40 amp....
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shocksridhar
In star i phase and i line is same ..,we are using star for distribution transformer so r phase curent and ry curent wil b same nly ..,u must undrstand frst...,
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srinivas v
P=root3•v.I/1000
=1•732*400*40/1000
=27.12
So your gender 27.12kva
| Is This Answer Correct ? | 0 Yes | 0 No |
why frequency should be constant?
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
cost of operation of which plant is least?
what is the function and use of oil filled cables specify its advantages and disadvantages
Merz-Price circulating current principles is more suitable for
can any one know is sbi interview based on merit or based on roll number
How much ph is maintained of water resistance starter for slipring induction motor ?
if a.c supply is given to the motor,, what happen?
Hi, I've just got into my electrical engineering course and I need some help with a question of mine here. During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz. From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?
How to calculate 33 kv panther conductor line losses.
1 Answers Construction, Orange,
How do we measure earth fault current in Generator Transformer(20/420kv),Station Transformer(20/11 kv) and Unit Transformers(20/11kv) for our plant system, since these don't have any Neutral earth Fault relay connected to their Neutral Earth? But for Unit Service transformers(11/.433 Kv) we have an Earth Fault Relay connected to its neutral earth.Why is such so?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)