Answer / sudhanva madhukar mahamuni
Hello To every One,
This is Sudhanva Madhukar Mahamuni Electrical Design
Engineer. The reason behind the same is not a alternator /
generator. The reason behind the same is diesel engine.
(Surprise!!!!!!!!!!)
Carefully read the catalog of DG Set for e.g. for 750kVA its
written as 750kVA / 600kW @ 0.8 pf. It means that alternator
size is 750kVA and 600kW is of Diesel engine. It means that
diesel engine can delivery only 600kW power. so if we like
to maintain the same then we need to keep 750kVA load on DG
@ 0.8 (750 x 0.8 = 600kW.
But assume that your load on alternator is 600kVA then you
are allow to improve your power factor till unity i.e. 1.
Therefore load on engine will be 600kVA x 1 = 600kW.
Summary : if multiplication of electrical load (in kVA) to
Power Factor will be upto or less than kW rating of diesel
engine then we can play with power factor i.e. lead or lag.
Note : If we will not do as above mentioned and improve the
power factor then engine will cease off (dead) i.e. cant
repair or modify.
For further clarification you can call me or mail me on
sudhanvamahamuni@structwel.com or sudhanvamahamuni@gmail.com
Regards
Mahamuni
9769317386
| Is This Answer Correct ? | 8 Yes | 1 No |
In DG ,we maintein pf .8 because , if pf decrease than
alternator has overload due to more current dron by load .
And if pf is increase ,than engine has overload due to
increase potational (volt ).
So maintain DG pf is 0.8 .
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vinodth
consider 1 transformer having the power 125mw,33kv...
1)p=125mw,
v=33kv,
cosQ=0.8
p=1.732VlIlcosQ
I=125000/1.732*33000*0.8
I=2733.7
2)cosQ=0.7
I=125000/1.732*33000*0.7
I=3124.29
loss=i*ir..if the pf reduces,then loss get increases...v
cant maintain the pf as unity,tats y the pf s maintained as 0.8
| Is This Answer Correct ? | 7 Yes | 5 No |
wat is d first thing to be seen 2 lay a cable in a particular area??
What are the diferences between ELCB and RCCB
from which formula we select a capacitor rating?
which element is neglected during fault calculation? a)resistance b)inductance c)capacitance d)reactance
Why we use RYB phase sequence?
why CRGO material used in transformer?
A IS TWICE AS GOOD A WORKMAN AS B AND TOGETHER THEY FINISH A PIECE OF WORK IN 14 DAYS.THE NUMBER OF DAYS TAKEN BY A ALONE TO FINISH THE WORK IS 1.11 2.21 3.28 4.42
HOW TO CALCULATE UPS BATTERY BACKUP TIME
can you plz send l&t aptitude questions if available its urgent plz plz plz
for a 11kv transmission line what capacity of CTs & PTs are required?
What is 100% protection of generator? Why 95% protection is used not 100%?
why the air gap is necessary in the transformer core
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)