why maintain the Dg PF is 0.8? Explain?
Answers were Sorted based on User's Feedback
Answer / sudhanva madhukar mahamuni
Hello To every One,
This is Sudhanva Madhukar Mahamuni Electrical Design
Engineer. The reason behind the same is not a alternator /
generator. The reason behind the same is diesel engine.
(Surprise!!!!!!!!!!)
Carefully read the catalog of DG Set for e.g. for 750kVA its
written as 750kVA / 600kW @ 0.8 pf. It means that alternator
size is 750kVA and 600kW is of Diesel engine. It means that
diesel engine can delivery only 600kW power. so if we like
to maintain the same then we need to keep 750kVA load on DG
@ 0.8 (750 x 0.8 = 600kW.
But assume that your load on alternator is 600kVA then you
are allow to improve your power factor till unity i.e. 1.
Therefore load on engine will be 600kVA x 1 = 600kW.
Summary : if multiplication of electrical load (in kVA) to
Power Factor will be upto or less than kW rating of diesel
engine then we can play with power factor i.e. lead or lag.
Note : If we will not do as above mentioned and improve the
power factor then engine will cease off (dead) i.e. cant
repair or modify.
For further clarification you can call me or mail me on
sudhanvamahamuni@structwel.com or sudhanvamahamuni@gmail.com
Regards
Mahamuni
9769317386
| Is This Answer Correct ? | 8 Yes | 1 No |
In DG ,we maintein pf .8 because , if pf decrease than
alternator has overload due to more current dron by load .
And if pf is increase ,than engine has overload due to
increase potational (volt ).
So maintain DG pf is 0.8 .
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vinodth
consider 1 transformer having the power 125mw,33kv...
1)p=125mw,
v=33kv,
cosQ=0.8
p=1.732VlIlcosQ
I=125000/1.732*33000*0.8
I=2733.7
2)cosQ=0.7
I=125000/1.732*33000*0.7
I=3124.29
loss=i*ir..if the pf reduces,then loss get increases...v
cant maintain the pf as unity,tats y the pf s maintained as 0.8
| Is This Answer Correct ? | 7 Yes | 5 No |
why we use copper earthing for neutral while for body GI.
1 Answers Chennai Metro Rail Limited CMRL, Valeo Lighting Systems India Private Limited,
what happen if drive input fail momentry at 48.5 HZ frequency?
why we use delta connection in transformer
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
1) Why distributiion system decided 11 kv, 33 kv, 66 kv, 132 kv, 220 kv, 400 kv, 2) In 3 Phase line terminal of capacitor, why used for power factor improvement. 3) Why used rating KVA in transformer?
why should we have to maintain pf in our site 0.9????????
how to control dc motor?
Why in power plant projects we see DOL starting method used for motors upto 160 kW instead of star delta method
how we can calculate which capacity capacitor bank we have to add for improve pf?
3 Answers Consultancy, JM Huber, Torrent Power,
WHY THE DIMENSION OF TWO SAME RATED MACHINE IS DIFFERENT ?
How instantanious short circuit current is calculated? its formula?
what is the difference between transformer and amplifier ??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)