In LT Line What is the minimum clearance required between
phase to phase busbar & between Phase to body of the panel?
Also between Neutral &phase, & Neutral & body of panel. as
per standards.
Answer / satish
phase to phase 26mm,phase to neutral 19mm ,neutral to body
20mm,phase to body 25mm,as rules-ANSCI.
| Is This Answer Correct ? | 8 Yes | 1 No |
why AC signals are represented by sinusoidal waveform?WHY other waveforms not used for representation
difference between substation & grid substation?
A 100W electric lamp is supplied from a 115V, 60HZ source. The peak instantaneous power dissipated in the lamp filament is
which technique servo motor tested o.k or faulty ?
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
Why human body feel electric shock?
what reactive how to maintain
1. what type of winding of slip ring ac induction motor rotor and why. 2. how the heating element use in two phase (415 volt)and what rating of element, you prefered.
What fomula is used to calculate: 1. rated frequency withstand voltage, and 2. rated lightning impulse withstand voltage.
Why we not use the impedance relay in protection of short transmission line ?
What is min and max voltage between earth and neutral/phase if it perfect earthing?
37 Answers Epoch, ISS, ITC Infotech, L&T, Power Works, Statex, Sterlite, Wipro,
What is the Surge for 1.1 Phase Induction Motor(For Eg.1Hp) 2.3 Phase Induction Motor(For Eg.1Hp) 3.AirConditioner(For Eg 1Ton) 4.Refrigerator(For Eg 180Ltr or 160kW) 5.Induction Cooker 4. Ceiling Fan
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)