about transformer oil material & Test name for the
measurement of its dielectric strength & wht will u do if
its dielectric strength goes low ?
Answers were Sorted based on User's Feedback
Answer / ravikumar.g
If the transformer oil dielectric strength is low we do the
Oil Filtration. ofter the oil filtration we tested the oil
by using the testing unit it will show 80 KV. if the oil
was fulley Carbonised so we have to replace the oil.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / alex
Transformer Dielectric oil is tested in a Test Cell, I have
a few of them at home that I inherited from the origional
designer of the test. They look like a thermos flask and you
fill them with a bit of the oil from the transformer and
insert a center section that sits 2mm away from the surface
of the inside of the flask all around (2mm dielectric gap
all round). It is held there with glass / Mica supports. 2KV
is then passed between the inner and outer surfaces (via the
oil) to test its dielectric strength. A high voltage bridge
is normally used to get accurate resistance readings. If
dielectric strenth is low due to contamination it is replaced.
| Is This Answer Correct ? | 3 Yes | 2 No |
what maximum range of star & delta in hp or kw ?
0 Answers Makkah Hilton Towers,
what is sustainable current of any conductors . a bare busbar or pvc cable has different sustainable current .
As a good company employee, can you report your supervisor to the company management if he or she is going against the company interest in his or her actions?
What is the full form of SON-T lamp?
features of hbc fuses
If a contactor need to replace with faulty one. what I want to check?
WHTA IS LIMT OF LEAKGE CURRENT OF 11 KV 1 CORE 1000SQ.MM. XLPE CABLE.LOAD ON CABLE IS AROUND 600AMP .LENGTH 500 MTRS.
what is the effect come when i changed the alternator exciter field winding DC palority(+ve & -ve)which is coming from AVR.
WHAT IS THE USE OF TERTIARY WINDING IN A STAR/DELTA TRANSFORMER ?
why we not used 11kva as a direct our electrnics component.
what are upstream faults and downstream faults in power system
If a surge divertor is required to be protected by 32 amp C Curve Circuit breaker does this limit the amount of protection from surges that you will acheive
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)