Where we cant instal mass flow meter.
Answer / carl_ellis
These remarks refer to the use or non-use of a coriolis mass
flow meter.
A coriolis mass flow meter should not be used
- where tight shutoff valve(s) cannot be installed upstream
and downstream for the purpose of stopping all flow so that
zeroing the coriolis flow meter can be accomplished (turning
off power to the pump is NOT the same as shutting off the
flow with a ball valve). Otherwise zero shift will plague
the operation.
- in a batch operation where the meter starts empty, then
fills, and at the end might run partially filled, unless
appropriate piping is implemented to keep the Coriolis flow
meter filled with fluid all the time.
- with suspended solids in a liquid medium that are abrasive
[abrasives erode the thin tube(s)]. Reducing the flow
velocity tends to reduce abrasion and erosion. A Coriolis
tube will quickly fail when it carries suspended solids like
sand. Unless of course, frequent replacement is just the
cost of doing business.
- with a corrosive medium that will corrode the flow tube
- with medium that is above the manufacturer's stated
process medium temperature (burns up the electronics)
- with a two phase media (liquids and gas or liquids that
will flash to vapor at the operating pressures and temperatures)
- with a medium that tends to solidify (Coriolis tubes are
very thin, very light and don't like to be brush cleaned)
unless periodic solvent cleaning is feasible.
- with a medium that tends to coat the tube, unless the
required solvent or mechanical cleaning is feasible.
- where the flow tube is subject to mechanical vibration
- when the meter is mounted where the flow is vertical down
- when the meter is mounted in horizontal piping at a high
point where gas/air can be trapped at a high point
- where the pressure drop across the flowmeter is higher
than the process can tolerate
- when the location is too close to another coriolis meter;
where each meter can be affected by crosstalk vibrations
from the other coriolis meter.
- hazardous or classified zones where the Coriolis' power
requirements exclude it from meeting hazardous area approval.
- for flow measurement requiring pipe sizes larger than
commercial coriolis meters (10 or 12" in 2014)
Carl Ellis
Measure First
Is This Answer Correct ? | 4 Yes | 0 No |
what is cascade controller ?
What information needs for Control Valve "sizing"
What is the load line in control valve?
Why 4mA-20mA current loop selected as standard ???
HOW TO DO PERFECT CALIBRATION OF DIFFERENTIAL PRESSURE TRANSMITTER FOR CLOSE VESSEL TANK LEVEL PURPOSE ???? AND HOW TO MAKE ZERO PRESSURE ?? Rosemount 2051 Pressure Transmitter with HART® Revision 5 and 7 Selectable Protocol BIENG USED !! HOW TO CALIBRATE FIELD SIDE DPT WITH THE HELP OF SPAN & ZERO PUSH BUTTONS ??
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
What is the out put of pressure switch & electronic pressure transmitter.
5 Answers ADMA OPCO, Al-Barrak,
what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC
1 Answers Bharat Biotech, TATA,
what is the difference between AUTOMATION AND INSTRUMENTATION?
how does we calibrate a square root flow transmitter ,give an example and explain it step by step like range calculation , calibration hook up series connection , zero check , and how to apply pressure , and if not geting proportional output then what should we do ?
please send data bank of quetions answers on analytical instrumentation.
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.