Where we cant instal mass flow meter.



Where we cant instal mass flow meter...

Answer / carl_ellis

These remarks refer to the use or non-use of a coriolis mass
flow meter.

A coriolis mass flow meter should not be used

- where tight shutoff valve(s) cannot be installed upstream
and downstream for the purpose of stopping all flow so that
zeroing the coriolis flow meter can be accomplished (turning
off power to the pump is NOT the same as shutting off the
flow with a ball valve). Otherwise zero shift will plague
the operation.

- in a batch operation where the meter starts empty, then
fills, and at the end might run partially filled, unless
appropriate piping is implemented to keep the Coriolis flow
meter filled with fluid all the time.

- with suspended solids in a liquid medium that are abrasive
[abrasives erode the thin tube(s)]. Reducing the flow
velocity tends to reduce abrasion and erosion. A Coriolis
tube will quickly fail when it carries suspended solids like
sand. Unless of course, frequent replacement is just the
cost of doing business.

- with a corrosive medium that will corrode the flow tube

- with medium that is above the manufacturer's stated
process medium temperature (burns up the electronics)

- with a two phase media (liquids and gas or liquids that
will flash to vapor at the operating pressures and temperatures)

- with a medium that tends to solidify (Coriolis tubes are
very thin, very light and don't like to be brush cleaned)
unless periodic solvent cleaning is feasible.

- with a medium that tends to coat the tube, unless the
required solvent or mechanical cleaning is feasible.

- where the flow tube is subject to mechanical vibration

- when the meter is mounted where the flow is vertical down

- when the meter is mounted in horizontal piping at a high
point where gas/air can be trapped at a high point

- where the pressure drop across the flowmeter is higher
than the process can tolerate

- when the location is too close to another coriolis meter;
where each meter can be affected by crosstalk vibrations
from the other coriolis meter.

- hazardous or classified zones where the Coriolis' power
requirements exclude it from meeting hazardous area approval.

- for flow measurement requiring pipe sizes larger than
commercial coriolis meters (10 or 12" in 2014)

Carl Ellis
Measure First

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is cascade controller ?

6 Answers  


What information needs for Control Valve "sizing"

1 Answers   Qatar Petroleums,


What is the load line in control valve?

1 Answers   IFFCO,


Why 4mA-20mA current loop selected as standard ???

1 Answers   IMCO, Reliance,


HOW TO DO PERFECT CALIBRATION OF DIFFERENTIAL PRESSURE TRANSMITTER FOR CLOSE VESSEL TANK LEVEL PURPOSE ???? AND HOW TO MAKE ZERO PRESSURE ?? Rosemount 2051 Pressure Transmitter with HART® Revision 5 and 7 Selectable Protocol BIENG USED !! HOW TO CALIBRATE FIELD SIDE DPT WITH THE HELP OF SPAN & ZERO PUSH BUTTONS ??

1 Answers   Bhel,






IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN

1 Answers   IFFCO,


What is the out put of pressure switch & electronic pressure transmitter.

5 Answers   ADMA OPCO, Al-Barrak,


what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC

1 Answers   Bharat Biotech, TATA,


what is the difference between AUTOMATION AND INSTRUMENTATION?

7 Answers  


how does we calibrate a square root flow transmitter ,give an example and explain it step by step like range calculation , calibration hook up series connection , zero check , and how to apply pressure , and if not geting proportional output then what should we do ?

0 Answers  


please send data bank of quetions answers on analytical instrumentation.

0 Answers  


Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)