Answer / shahid
It depends on Voltage rating.
As 11 KV
Example.
we used Transformer 11/0.433 KV ,500 KVA, Its Primary side
26.2 A and its secondary side 666.2 A.
Its mean 1A in HT equivalent to 25.4 A
Is This Answer Correct ? | 139 Yes | 22 No |
Answer / j.prabhakaran
if we knows the primary & secondary turns or voltage ratio
of transformer by using the formula
n1/n2=i2/i1=v1\v2
we could find the answer..
Is This Answer Correct ? | 11 Yes | 5 No |
what is fundamental difference between voltage and current
i am studying in final year can i allowed for 23rd UES of Indian army
why we are using DC violtage for testing of cables....which is used in HV AC applicatons...
which connection is there in a rotor of the motor
2 Answers All Trades Electrical, HAL,
Can any one explain me about 2 phase motors ?
WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT
on which power factor synchronous motor run
how much current (in MW)can be carried max. through S/C dog & Panther Conductor ?
In 3phase supply Voltage will come around 370v then what will happen?(mean what will effect on electrical equipment like AC,UPS,Motors.)
What are differences between Voltage, EMF & Potential difference ?
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
what is differnt between metering CTs an protection CTs