What are protection of power transformer?
Answer / sakthi
Internal
Winding Phase-Phase,
Phase-Ground faults
Differential (87T), over current (51, 51N)
Restricted ground fault protection
(87RGF)
Winding inter-turn
faults
Differential (87T), Buchholz relay,
Core insulation failure,
shorted laminations
Differential (87T), Buchholz relay,
sudden pressure relay
Tank faults Differential (87T), Buchholz relay and
tank-ground protection
Overfluxing Volts/Hz (24)
External
Overloads Thermal (49)
Overvoltage Overvoltage (59)
Overfluxing Volts/Hz (24)
External system short
circuits
Time overcurrent (51, 51G),
Instantaneous overcurrent (50, 50G)
Is This Answer Correct ? | 6 Yes | 0 No |
What are the advantages and disadvantages of oil filled transformers?
2 Answers Mercantile Marine Department, Studio College,
What is the maximun current carring capacity in per phase for three pole 100anps rating ncb
what is the power factor used by the PHCN in nigeria? 2. what is the difference between an alternator and generator. 3. Generation of poweris in KV but how is transmission is in MW. 4.If the transmission of power is 20,000MW how can it be increaesed to 80,000MW
the transient state stability limit of a system wherin power is transmitted throgh a double transmission line is (a)equal to steady state stability limit (b)more than its steady state stability limit (c)less than than its steady state stability limit (d)equal to its dynamic stability limit
our plant maximum demand has 500 kva.need to suggest me to maintained pf 0.98.how much capacitor bank will be connect to the supply line.
What is master trip relay? How does it work?
If the (Motor control center)Panel work on field the relay used in panel in the case this will be damage and no indication provide on panel.fault occur in panel and MCB will not trip. how happen the relay damage in panel and what effect of panel.
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
can you any one give exact mathematical relation between AC current and DC current?
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
what is meant by MCB and MCCB? and what its full form?