can we correct the p.f.of ac generator?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Yes.By varying the excitation i.e. the terminal voltage.If
the voltage of the generator is more than the grid
voltage ,the pf will be lagging and the vice versa.But the
pf has to be maintained at 0.9 to 0.98 lag ,for system
stability.A poor pf results in higher armature current
which is also not desirable
Is This Answer Correct ? | 22 Yes | 2 No |
Answer / mohammad afzal
yes, we can correct the p.f of ac generator by manually
varying the volatage of generator and exciting current of
the field rotor. the recommended range of the p.f should
between 0.9 to 0.98 lagging. poor p.f more armature current
and increase in temperature of stator which is not
desirable.
Is This Answer Correct ? | 1 Yes | 0 No |
Can someone tell me how to calculate the size of a power cable? What are the factors involved in cable sizing?
why constant voltage transformer should be start without load? and if started then what will happen?
What is the permissible value of earth resistance!
what are the functions & ratings of panels mentioned below: 1. Main LT Panel(MLTP) 2. Motor Control Centre(MCC) 3.Feeder pillars 4.Busducts
losses in transmission lines ?
why resistive load has unity power factor,inductive load lagging and capacitive load leading power factor?
what is total power generation in tamilnadu What are the methods used powerfactor improved? which place DC transmission line usde?
what is stiffness factor
i have done diploma and btech in EE and live in Chandigarh so kindly help me how can i make my competency certificate in my area.
What is the meaning of EDO in DG panels?
1 Kva = How many KW
the resstance of a thermistor is 5000 ohm at 25degreeC and coefficient is .04/degCel. A measurement with lead resitance of 10 ohm will cause an error of