What is LT? And specify the range of voltage?
Answers were Sorted based on User's Feedback
Answer / mohd. karim
LT - Low Tension (Low Voltage)
It depend on our reference voltage...It means our system is
440KV than we say 33KV & 11KV &3.3KV are LT for our System.
If our system is based on 11KV (Higest Voltage of System)
then 3.3KV & 415V is LT for based voltage.
| Is This Answer Correct ? | 31 Yes | 9 No |
Answer / naresh
LT refers Low Tension. Its range is as follows....
1) For Single Phase it is 240V and
2) For Three Phase it is 415V as per Indian standards.
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / amit upadhyay dscl
LT is low tension side,and the specify range is 415v
| Is This Answer Correct ? | 25 Yes | 8 No |
Answer / avnish sharma
Upto 650 V the Power Supply is considered LT ( Low Tension), but 650 V is not a general utility voltage.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / ashish jain
any voltage level below 1 KV is called LT(low tension). in
industry generally it 415 V, mining it is 650 V.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / hasan mehdi
LT is Low Tension, and specify the range of voltage 440V.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / srinivas
Up to 650 V ,AC power supply is called L.T power, as per IE rules.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / veresh g
# 1 LT is low tension side,and the specify range is 415v
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / k.prabhakar reddy
LT means Low tension Voltage.the range of LT Voltage is less
than 3.3KV and above 3.3KV is High tension Voltage
| Is This Answer Correct ? | 0 Yes | 1 No |
low tension power supply . the rete of voltage is 230V
according to india standerd
| Is This Answer Correct ? | 8 Yes | 16 No |
i need to give section engineer (electrical engineer) for RRB. Please suggest some book
Does power factor vary with speed?If yes, how?If not, why?
What is resonant frequency?
AIR GAP IS TERMED AS USEFUL. WHY?
We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.
What happens when two positively charged material is placed together?
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
why transformer is rated in KVA ?
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
why we use to transmit the power in three phases intead of single phase ?
When we need start the motor by method of star delta which size (KW or HP)motor should must be operate in Star Delta Method,
if flow of electrons is current then why their direction are different???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)