why temperature transmitter is showing ambienttemp.but 21.5ma.
alarm AO showing at the display &how to sloves this problem.
Answers were Sorted based on User's Feedback
Answer / carl_ellis
When you need troubleshooting assistance you need to supply
certain critical information:
1) Has the device ever worked correctly before for some
time period and then failed?
Or is this a first time commissioning issue?
2) What is the brand name and model number of the device?
3) Because all devices have an input and an output, exactly
what each is (is your sensor one thermocouple, two
thermocouples, or one RTD?)
- You do tell us the output is 21.5mA.
4) What are the error codes or what the error symptoms?
- You mention the display shows ambient temperature
5) What you've done to troubleshoot the problem, like
substitute a known source (simulator) and the result
was . . . . ?
Evaluation:
ambient temperature: A short circuit (a wire) across the
terminal inputs of a thermocouple input will display near-
to-ambient temperature, specifically the temperature of the
terminal block connectors. The value is the cold junction
compensation (CJC) temperature.
Some high end transmitters will show the CJC temperature.
Is the display stuck on the CJC temperature, rather than
its input? Is there a short across the (+) and (-) input
terminals?
21.5mA is a very common fail-safe alarm level, outside the
normal 4-20mA range, but indicating that there is a serious
fault in the transmitter setup or operation. If the fail-
safe is configured for fail high, an open input (among many
other things) could cause the fault.
Smart transmitters generate an error code and save it. If
the transmitter has HART, the error code is in one of the
diagnostics registers, but a HART communicator is needed to
access the error code.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
A short circuit (both thermocouple wires touching each
other) in the thermocouple extension wire leads will create
an ambient or near-ambient temperature reading, but I am
unaware of any temp transmitter that can detect that problem
and go to fault mode at 21.5mA.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
What is SCADA ? WHAT is it role in DCS ?
What is the exact output of eddy current proximity probe? For vibration mesurment?
What is passive connection of instrument in different type of I/O module
what is the approximate cost of U tube manometer having range 1000mmwc to 1000mmwc?
what is the meaning of HART ?
How to calculate the Range of level transmitter ?
in mass flow meter what is drive friquancy ?
What are the error values can accepted in flow transmitter calibration?could u give any formula for this?
Please can anybody help for control valve sizing step by step procedure?
What skill/s does the Instrument Technician has?
how the 4 to 20 mA signal goes to any controller/indicator,and what is the role of voltage ,12/24 and how to do connection of it, in controller.
why use on -off control valve in glove valve