Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why temperature transmitter is showing ambienttemp.but 21.5ma.
alarm AO showing at the display &how to sloves this problem.

Answers were Sorted based on User's Feedback



why temperature transmitter is showing ambienttemp.but 21.5ma. alarm AO showing at the display &..

Answer / carl_ellis

When you need troubleshooting assistance you need to supply
certain critical information:

1) Has the device ever worked correctly before for some
time period and then failed?

Or is this a first time commissioning issue?

2) What is the brand name and model number of the device?

3) Because all devices have an input and an output, exactly
what each is (is your sensor one thermocouple, two
thermocouples, or one RTD?)
- You do tell us the output is 21.5mA.

4) What are the error codes or what the error symptoms?
- You mention the display shows ambient temperature

5) What you've done to troubleshoot the problem, like
substitute a known source (simulator) and the result
was . . . . ?

Evaluation:
ambient temperature: A short circuit (a wire) across the
terminal inputs of a thermocouple input will display near-
to-ambient temperature, specifically the temperature of the
terminal block connectors. The value is the cold junction
compensation (CJC) temperature.

Some high end transmitters will show the CJC temperature.
Is the display stuck on the CJC temperature, rather than
its input? Is there a short across the (+) and (-) input
terminals?

21.5mA is a very common fail-safe alarm level, outside the
normal 4-20mA range, but indicating that there is a serious
fault in the transmitter setup or operation. If the fail-
safe is configured for fail high, an open input (among many
other things) could cause the fault.

Smart transmitters generate an error code and save it. If
the transmitter has HART, the error code is in one of the
diagnostics registers, but a HART communicator is needed to
access the error code.

Carl Ellis
Measure First

Is This Answer Correct ?    2 Yes 0 No

why temperature transmitter is showing ambienttemp.but 21.5ma. alarm AO showing at the display &..

Answer / carl_ellis

A short circuit (both thermocouple wires touching each
other) in the thermocouple extension wire leads will create
an ambient or near-ambient temperature reading, but I am
unaware of any temp transmitter that can detect that problem
and go to fault mode at 21.5mA.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is metal of piston ring

0 Answers   MahaGenco,


what is the difference between active & reactive power?

0 Answers  


What is the working principle of oxygen analyzers(zirconium oxide type) used in CFBC boilers?

3 Answers   Bajaj, Kohinoor, Wartsila,


What is the detail function of I/O card in DCS ? Why we dont use the I/O directly with controller?

3 Answers   Kekran Mekran, TCE,


Hot calibrate a level transmitter (wet & dry legs)?

1 Answers   Honeywell, IEC,


When we will do simulation for I/P?IF WE DO SIMULATION through which way either series or parallel?

1 Answers   TVS,


Why is the orifice tab provided?

0 Answers  


Do you have reference list?

0 Answers  


What is the difference between uv and ir scanners? and what is the workig principle of both

0 Answers  


How earthing can be checked????

0 Answers  


What are the application of bernoulli’s theorem?

0 Answers  


How do you measure g's?

5 Answers   Aramco, GNFC, HPCL, Polmon, Thermax,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)