why temperature transmitter is showing ambienttemp.but 21.5ma.
alarm AO showing at the display &how to sloves this problem.
Answers were Sorted based on User's Feedback
Answer / carl_ellis
When you need troubleshooting assistance you need to supply
certain critical information:
1) Has the device ever worked correctly before for some
time period and then failed?
Or is this a first time commissioning issue?
2) What is the brand name and model number of the device?
3) Because all devices have an input and an output, exactly
what each is (is your sensor one thermocouple, two
thermocouples, or one RTD?)
- You do tell us the output is 21.5mA.
4) What are the error codes or what the error symptoms?
- You mention the display shows ambient temperature
5) What you've done to troubleshoot the problem, like
substitute a known source (simulator) and the result
was . . . . ?
Evaluation:
ambient temperature: A short circuit (a wire) across the
terminal inputs of a thermocouple input will display near-
to-ambient temperature, specifically the temperature of the
terminal block connectors. The value is the cold junction
compensation (CJC) temperature.
Some high end transmitters will show the CJC temperature.
Is the display stuck on the CJC temperature, rather than
its input? Is there a short across the (+) and (-) input
terminals?
21.5mA is a very common fail-safe alarm level, outside the
normal 4-20mA range, but indicating that there is a serious
fault in the transmitter setup or operation. If the fail-
safe is configured for fail high, an open input (among many
other things) could cause the fault.
Smart transmitters generate an error code and save it. If
the transmitter has HART, the error code is in one of the
diagnostics registers, but a HART communicator is needed to
access the error code.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
A short circuit (both thermocouple wires touching each
other) in the thermocouple extension wire leads will create
an ambient or near-ambient temperature reading, but I am
unaware of any temp transmitter that can detect that problem
and go to fault mode at 21.5mA.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
How earthing can be checked????
draw shematic diagram of c/v positioner(smart type)?
What is the start up procedure of desalter
Why we use the double acting control valve in flow line?
Types of contol loops
What is the purpose of RS Networks
what is the principal of flow transmeter,level trans meter,presser transmeter?
1. What is the main differences between GE Mark IV and Mark V Turbine Control System? 2. what is the main differences between GE Mark V and Mark VI?
How to calibrate a orifice differential pressure flow transmitter in process?
Lists Different types of Tappings.
Boolean algebra
Why plc require in analog input 4-20amp & 0-10 volt?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)