Can I parallel 1 MVA generator with 1kVA Generator? if V, F,
Ph Seq and Ph angles are same
Answers were Sorted based on User's Feedback
Answer / sunil kumar kr
I feel the question is an imaginary one as normally no such requirement arises. However the answer is yes. Once these generators are synchronised it will share the load based on the droop settings.
Is This Answer Correct ? | 7 Yes | 1 No |
what is extra low voltage system
How do you reverse the direction of rotation of a FAN?
what is difference between KW and KVA
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
why is corona loss greater in a stranded conductor as compared to a solid conductor ?
What is rccb?
what do u mean by knee point voltage?
PLEASE INFORM ABOUT THE IDEAL TEST RESULTS OF MAGNETIC BALANCE TEST OF TRANSFORMER 33/11 kv DELTA-STAR T/F
what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
percetans
What determines the thermal loading on the motor?