SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN
THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE
CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS
BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I
REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT
STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS
INITILAZIATION PLEASE HELP ME READRING THIS?
Answers were Sorted based on User's Feedback
Answer / warren emmett
Firstly, you should use a loop simulator and simulate the
Milliamp range to the dcs 0 to 20 or 4 to 20 do this in 25%
steps.If the dcs responds to the signal then the problem is
with the radar transmitter. If the problem persists when
simulating the the problem is on the Input card. Could be a
zero volt issue, a faulty input card or a wiring issue
could even be software related. To remedy the radar if that
is deemed faulty then consult the manual, you might need to
adjust parameters or do mapping of the vessel when it is
empty. Hope this helps
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / hirensinh
Set up the Parameter,Basically you know Tank is Empty or
Tank is Partially full.
Parameter set
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / prakash malviya
first u have 2 remove o/p wires of 4-20 ma then connect ma source with parellel this.then give 4& 20 ma...at 4 u see 0 %lvl & at 20 u find 100% lvl in dcs.if can't then u have 2 check from dcs side.in dcs check AI card particular channel for this.check wires grounding.
2nd condition if u find proper response in dcs with ma given to o/p wires..then go to the radar menu ..go to configuration..in that u find tank lvl...select full...then save it..
| Is This Answer Correct ? | 0 Yes | 0 No |
can anyone tell free downloads website for fundamentals and principle of basic pressur,temperature,level and flow
Which are all the commonly used Bordon tubes in the pressure gauges. Do any one use ASTM A 312 tubes for this purpose?
Condensation within a sight glass? Would you expect there to be more problems when using a sight glass if there is condensation on the inside or the outside of the glass, and why?
In case of Transmitter's(e.g.Ultrasonic Flow meter ) we have an normal practise of selction of upstream and downstream distance such as (20D and 5D ).can anyone please let me know whow to calculate "D" ?? i guess it refers to pipe thickness is t right ?
what is diffrence between analog card and digital card in plc.how analog card work,Please explain in detail.Please send it on abhi_vyas@sify.com
when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )
How does a redundant controller comes in line when the main controller fails??
what is the difference between -24 : +24 & 0:24 and where it use?
What is the difference between pneumatic and electro pnematic positioner?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
what is the difference between Ethernet unmanaged and managed Switch?
What is zone,loop/fire alarm system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)