SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN
THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE
CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS
BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I
REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT
STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS
INITILAZIATION PLEASE HELP ME READRING THIS?
Answers were Sorted based on User's Feedback
Answer / warren emmett
Firstly, you should use a loop simulator and simulate the
Milliamp range to the dcs 0 to 20 or 4 to 20 do this in 25%
steps.If the dcs responds to the signal then the problem is
with the radar transmitter. If the problem persists when
simulating the the problem is on the Input card. Could be a
zero volt issue, a faulty input card or a wiring issue
could even be software related. To remedy the radar if that
is deemed faulty then consult the manual, you might need to
adjust parameters or do mapping of the vessel when it is
empty. Hope this helps
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / hirensinh
Set up the Parameter,Basically you know Tank is Empty or
Tank is Partially full.
Parameter set
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / prakash malviya
first u have 2 remove o/p wires of 4-20 ma then connect ma source with parellel this.then give 4& 20 ma...at 4 u see 0 %lvl & at 20 u find 100% lvl in dcs.if can't then u have 2 check from dcs side.in dcs check AI card particular channel for this.check wires grounding.
2nd condition if u find proper response in dcs with ma given to o/p wires..then go to the radar menu ..go to configuration..in that u find tank lvl...select full...then save it..
| Is This Answer Correct ? | 0 Yes | 0 No |
What is calibration?
What is DeltaV?
Technician A says that a fuel tank sending unit will have a high resistance only when the tank is full. Technician B says that its resistance when the tank is full depends on whether the sending unit is designed for use with a bimetallic gauge or with a magnetic gauge. Who is correct?
How can you differentiate Instrumentation to Electrical?
if i want buy a pressure gauge then witch parameter i look
Why we use 3-15 psi air for control valve input?
I want to measure and control level in tank of size 10*5 filled with gasoline, so plz give me the solution with clear details. how to select transmitter and sensors.
WHY THE DEGREE OF VALVE PLUG AND VALVE SEAT IS SLIGTLY DIFFERENT I CONTROL VALVE TRIM DESIGN
IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?
How can we calibrate pressure and flow transmitter in the field(online)?
how to measure draft pressure in transmitter pl. give its single line digram
HOW TO CALCULATE WAKE FREQUENCY FOR THERMOWELL???WITH OUT SOFTWARE..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)