Answer / 7anoter4
According to UL-1072 ch.57.5 insulation resistance of an
insulated conductor will be:
R=1000*K*log10(D/d)/L
D=insulated core diameter d=conductor diameter. L=cable
length.
The minimum permissible insulation resistance will be:
K=20000 Mohm/1000 ft. then L=cable length in ft. or K=6100
Mohm/km then L will be in m.
Let's say we have a 1*240 sqr.mm copper conductor 11 kV
XLPE insulated cable.
According to IEC 60502-2 [BS6622] insulation thickness=3.4
mm.
The conductor diameter is about 20 mm.
Then D=20+3.4*2=[approx.]27 mm.
R=1000*6100*log10(27/20)/m=7.95*10^5 Mohm/m or 795 Mohm/km.
| Is This Answer Correct ? | 0 Yes | 1 No |
What willbe change in programming when we use 5/3 solenoid inplace of 5/2 in operating of a cylinder?
what is the use of piston rings in the engine used for a generator...........
What is a pulse transformer?? Can it be called as a dc transformer??
The speed of a dc motor can be controlled by the variation of 1. armature voltage. 2. field current. 3. armature circuit resistance. 4. angle of brush shift. Which of the statements given above are correct? (a) 1,2 and 3 (b) 2,3 and 4 (c) 1,3 and 4 (d) 1,2 and 4
How to calculate the actual 3phase power, if the load current of each phase is not balanced
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
how many BUSBAR is in electrical system?
My switchgear busbar is rated at 2000A and just imagine the actual load on busbar is 1000A. From that busbar there are 10 outgoing feeders. Now the question is will the load be 1000A on each outgoing feeder or 100A per outgoing feeder. 2nd thing how do i calculate the load on individual feeder. Thanks for your time. Please provide some clarification on this issue.
What will be the direction of rotation of a Alternator in case it goes in motoring action when connected with grid ?
we have two motors 1250kW,6.6kV to be coupled on the same shaft ,so please provide assistance for their synchronisation.
What will happen if a dc source is given to a tubelight. Will it work or wont it work....
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)