how can calibrate vacume trasmitter by HART COMMUNICATOR ?
Answers were Sorted based on User's Feedback
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. go to process parameter and change the follwing
parameters
LRV:760mmhg
URV:0mmhg
then press send .then cross check the transmitter with
master pressure calibrator
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / senthilkumar
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. LRV= (-)760 mmHG URV= 0 mmHG
6. apply pressure 760 mmHG to low pressure side and see the
output it will show 20mA.
Is This Answer Correct ? | 2 Yes | 5 No |
if found error in magnetic flow meter?how can we adjust?
2 Answers ANI Instruments, Techint,
Can any one send me IOCL instrumentation question papers.. i dont know the pattern of the questions and what to prepare can any one help me on this .. my email id is anwarnishil@gmail.com
1.what is the role of proportional comtroller in pid controller?2.How do u calibrate the control valve?
Control valve question what is the meaning of cauge.?what is the use of cauge?
Where is the flow transmitter installed with respect to control valve, state reason.
What are the key components of control loop?
What is the difference between HMI and SCADA and MMI
what is input and output cards of plc needs to be hot swappable mean
any body please send me the old question papers of ongc test.
i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500 ltr/hr.) what should i do?
How can I zero check of wet leg type DP Tx ?
What is zone,loop/fire alarm system?