how can calibrate vacume trasmitter by HART COMMUNICATOR ?
Answers were Sorted based on User's Feedback
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. go to process parameter and change the follwing
parameters
LRV:760mmhg
URV:0mmhg
then press send .then cross check the transmitter with
master pressure calibrator
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / senthilkumar
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. LRV= (-)760 mmHG URV= 0 mmHG
6. apply pressure 760 mmHG to low pressure side and see the
output it will show 20mA.
| Is This Answer Correct ? | 2 Yes | 5 No |
What is the exact differences between HART,FOUNDATION FIELDBUS,PROFIBUS?
what is The specifications for oriface instalation
i have an interview in Qatar Petroleum. So please provide the all details abt fire & gas systems
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
Why not come out analog output in ABB EL3020 when display show correct value
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
Can anybody tell which type of quections are asked in interview for projects? plz give its urgent.....!
What is the difference between HMI and SCADA and MMI
Name some of the common protocol use in automation.
in rotark mov in display err msg showing how to remove the error
I WANT SECURITY PAPER MILL, HOSHANGABAD TEST PAPER.KINDLY SEND TO MY MAIL ID
Why we use 250 ohm resister in series hart communicator?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)