If Solenoidal valve works in manual mode but not in Auto
mode. What should be the problem?
Answers were Sorted based on User's Feedback
Answer / satishkumar
first, check the SOV coil is working or not and then check
the power supply from DCS to sov coil.
Is This Answer Correct ? | 18 Yes | 5 No |
Answer / raffi
Signal(Soft PB) for SOV to open in Manual and Auto are same (DO)
While your are running in AUTO. it is working with interlock/logic i.e feedback from other IOs
While in Manual mode you should press the SOV button to open after change the mode to manual
If it not working in AUTO then Check the malfunction of feedback signal IO card or carryout the loop checking for feedback signal to sort out the issue
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / fellyc
Assume that both Manual Command (PB) and Auto signal comes
from the DCS ( Same DO).
If it works in Mamual Mode and not in Auto Mode, then check
the logic for an interlock or permissive.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / ganapathi s.b
First check DO out put came or not. if signal not come check Do module, if signal came then check sov coil Resistance value
either open or short.this is main problem of not working in Auto mode.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raja
Need to be check the DCS I/O cart the DI cart digital output cart some time give fault signel the I/O cart malfunction
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sriram
Either manual mode u operate from dcs then the DO card is good. so check the interlock
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / hansdas b.jaiswal
If you are operate solenoid valve with out load so please
connected it a power cylinder or actuator some time
solenoid valve not works in auto mode with out load.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / govarthan
whether card is not working sov not working in man mode also i think ter s an external interlock check it..
Is This Answer Correct ? | 1 Yes | 8 No |
What output voltage the proximity switch shows when it is in open enviornment?
What are the characteristics of Control Valve
what is the differnce between PLC & DCS
why 4 to 20 ma? why cant some other range?
how to calculate static pressure in a pipe line,when we know the DP(differential pressure) in the line, area of the pipe? please any one tell me the relation between them..?
How to Calibrate Level Switch in field
what is actual difference between pressure Transducer & Pressure Transmitter.
What care will you take in the installation of control valves,SCADA,DCS and FOC in Oil and Gas Project?
What is exact difference between the panel earthing and system earthing in DCS system. What is the value of resistence.
can we control operation of PLC from operator station?
How to connect field devices to PLC and DCS using a FIELD BUS, DP,MOD BUS(please tell me any extra interfce or adopters need in this case if we use remote i/o s)
anybody having Qatar Petroleum questions for instrument Technician offshore ....please send me