Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


If Solenoidal valve works in manual mode but not in Auto
mode. What should be the problem?

Answers were Sorted based on User's Feedback



If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / satishkumar

first, check the SOV coil is working or not and then check
the power supply from DCS to sov coil.

Is This Answer Correct ?    18 Yes 5 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / raffi

Signal(Soft PB) for SOV to open in Manual and Auto are same (DO)
While your are running in AUTO. it is working with interlock/logic i.e feedback from other IOs

While in Manual mode you should press the SOV button to open after change the mode to manual

If it not working in AUTO then Check the malfunction of feedback signal IO card or carryout the loop checking for feedback signal to sort out the issue

Is This Answer Correct ?    8 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / fellyc

Assume that both Manual Command (PB) and Auto signal comes
from the DCS ( Same DO).
If it works in Mamual Mode and not in Auto Mode, then check
the logic for an interlock or permissive.

Is This Answer Correct ?    3 Yes 2 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / ganapathi s.b

First check DO out put came or not. if signal not come check Do module, if signal came then check sov coil Resistance value
either open or short.this is main problem of not working in Auto mode.

Is This Answer Correct ?    1 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / raja

Need to be check the DCS I/O cart the DI cart digital output cart some time give fault signel the I/O cart malfunction

Is This Answer Correct ?    4 Yes 4 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / sriram

Either manual mode u operate from dcs then the DO card is good. so check the interlock

Is This Answer Correct ?    0 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / hansdas b.jaiswal

If you are operate solenoid valve with out load so please
connected it a power cylinder or actuator some time
solenoid valve not works in auto mode with out load.

Is This Answer Correct ?    0 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / govarthan

whether card is not working sov not working in man mode also i think ter s an external interlock check it..

Is This Answer Correct ?    1 Yes 8 No

Post New Answer

More Instrumentation Interview Questions

I have observed in field instrumentation work... I remove the fuse of an analog transmitter then it shows 7.75 kg/sq cm (which is practically wrong value)in DCS and when put the fuse it shows 0 in dcs. Then cheach the field transmitter termination and found moister. clean that and then it shows 1.1 kg/ sq cm which is right value. Please describe the above phenomenon.

1 Answers  


Why plc require in analog input 4-20amp & 0-10 volt?

0 Answers  


What is SCADA ? WHAT is it role in DCS ?

3 Answers   Honeywell,


why we us isolation barrier in hazardous area how it works to protect the area and please clarify its current flow.

0 Answers  


Working principle capacitance type level transmitter

3 Answers  


what is the square root flow transmitter formulla ?

2 Answers  


find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s

0 Answers  


what is hot loop check and cold loop check.

3 Answers   Bapco Bahrain Petroleum Company,


How to check the SCAN time of DCS ,n dont give therotical answers .How to check the SCAN time of DCS during FAT?

2 Answers  


WHAT REASEAN USE TRANSMETER TWO WIRE & FOUR WIRE

5 Answers   Kentz,


how to calculate control valve bonnet size?? or how to select its material?

0 Answers   Jacobs,


Which standard of hazardous area classification used in India?

1 Answers   Orchid,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)