If Solenoidal valve works in manual mode but not in Auto
mode. What should be the problem?
Answers were Sorted based on User's Feedback
Answer / satishkumar
first, check the SOV coil is working or not and then check
the power supply from DCS to sov coil.
| Is This Answer Correct ? | 18 Yes | 5 No |
Answer / raffi
Signal(Soft PB) for SOV to open in Manual and Auto are same (DO)
While your are running in AUTO. it is working with interlock/logic i.e feedback from other IOs
While in Manual mode you should press the SOV button to open after change the mode to manual
If it not working in AUTO then Check the malfunction of feedback signal IO card or carryout the loop checking for feedback signal to sort out the issue
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / fellyc
Assume that both Manual Command (PB) and Auto signal comes
from the DCS ( Same DO).
If it works in Mamual Mode and not in Auto Mode, then check
the logic for an interlock or permissive.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / ganapathi s.b
First check DO out put came or not. if signal not come check Do module, if signal came then check sov coil Resistance value
either open or short.this is main problem of not working in Auto mode.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raja
Need to be check the DCS I/O cart the DI cart digital output cart some time give fault signel the I/O cart malfunction
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sriram
Either manual mode u operate from dcs then the DO card is good. so check the interlock
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / hansdas b.jaiswal
If you are operate solenoid valve with out load so please
connected it a power cylinder or actuator some time
solenoid valve not works in auto mode with out load.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / govarthan
whether card is not working sov not working in man mode also i think ter s an external interlock check it..
| Is This Answer Correct ? | 1 Yes | 8 No |
please can anyone tell me in detail, what's mean by open loop and close loop?
How to measure high frequency using thermistor
What is NAMUR standard and why its allways reletad with Sollenoid
in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com
THE OUTPUT OF A CURRRENT TRANSMITTER OR A PNEUMATIC TRANSMITTER HAS A LIVE ZERO?EXPLAIN
i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?
how to use one 4-20mA signal for two indicater or controller & give necessary precaution.
what is the difference between transmitter and converters?
How would i calibrate a new commissioned flow transmitter???
Specify for Cables - Flame Retardant and Fire Resistant?
what is the approximate cost of U tube manometer having range 1000mmwc to 1000mmwc?
how to install the Ph and Conductivity analyser? is there are any procedures which has to be maintained.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)