If Solenoidal valve works in manual mode but not in Auto
mode. What should be the problem?
Answers were Sorted based on User's Feedback
Answer / satishkumar
first, check the SOV coil is working or not and then check
the power supply from DCS to sov coil.
| Is This Answer Correct ? | 18 Yes | 5 No |
Answer / raffi
Signal(Soft PB) for SOV to open in Manual and Auto are same (DO)
While your are running in AUTO. it is working with interlock/logic i.e feedback from other IOs
While in Manual mode you should press the SOV button to open after change the mode to manual
If it not working in AUTO then Check the malfunction of feedback signal IO card or carryout the loop checking for feedback signal to sort out the issue
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / fellyc
Assume that both Manual Command (PB) and Auto signal comes
from the DCS ( Same DO).
If it works in Mamual Mode and not in Auto Mode, then check
the logic for an interlock or permissive.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / ganapathi s.b
First check DO out put came or not. if signal not come check Do module, if signal came then check sov coil Resistance value
either open or short.this is main problem of not working in Auto mode.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raja
Need to be check the DCS I/O cart the DI cart digital output cart some time give fault signel the I/O cart malfunction
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sriram
Either manual mode u operate from dcs then the DO card is good. so check the interlock
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / hansdas b.jaiswal
If you are operate solenoid valve with out load so please
connected it a power cylinder or actuator some time
solenoid valve not works in auto mode with out load.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / govarthan
whether card is not working sov not working in man mode also i think ter s an external interlock check it..
| Is This Answer Correct ? | 1 Yes | 8 No |
I have observed in field instrumentation work... I remove the fuse of an analog transmitter then it shows 7.75 kg/sq cm (which is practically wrong value)in DCS and when put the fuse it shows 0 in dcs. Then cheach the field transmitter termination and found moister. clean that and then it shows 1.1 kg/ sq cm which is right value. Please describe the above phenomenon.
Why plc require in analog input 4-20amp & 0-10 volt?
What is SCADA ? WHAT is it role in DCS ?
why we us isolation barrier in hazardous area how it works to protect the area and please clarify its current flow.
Working principle capacitance type level transmitter
what is the square root flow transmitter formulla ?
find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s
what is hot loop check and cold loop check.
3 Answers Bapco Bahrain Petroleum Company,
How to check the SCAN time of DCS ,n dont give therotical answers .How to check the SCAN time of DCS during FAT?
WHAT REASEAN USE TRANSMETER TWO WIRE & FOUR WIRE
how to calculate control valve bonnet size?? or how to select its material?
Which standard of hazardous area classification used in India?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)