URGENT PLEASE//////////A WORK SHOP IS HAVING A 100 KVA
TRANSFORMER 11KV/415 VOLTS,
AND THE CONNECTED LOAD OF THE WORK SHOP IS 80 KW WITH
INDUCTIVE LOADS, LIGHTING LOADS,ETC.,
HOW MANY EARTH ELECTRODES ARE NEEDED AND WHAT IS THE EARTH
RESISTANCE OF EACH EARTH ELECTRODE AND COMBINED EARTH
RESISTANCE in normal soil. AT 11 KV SIDE AND AT LT SIDE. HOW
TO CALCULATE.
Answer / sudhakar g
For any transformer it is better to install two for body
eathing and two for Neutal earthing
Body Earthing: GI pipe 40mm dia using charcoal and salt
like this
Neutral Earthing: Copper plate 600x600x3 mm size for
netural earthing with all neccesary materials
After completion of Earthing you need to check the earth
resistance value for these earthing it should be below 3ohms
I think these are the neccasary requiremnts for your
trasnformer
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the difference b/w pvc cu conductor and cu breaded wire..?
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect each capacitor to busbar??
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
what is skin effect and corona discharge ?
What is shutdown of electrical sub station?
why is that a 4*4mm cable,is always powdered internally
What is core CT & it's function?
what is sevice settings for mccb?How can be it setted?
rating of ups??
in telecom we are using neutral?
why the rating of dc generator is in kw where as rating of alternator is in kva?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)