a 650 KVA diesel generator is 1500 rpm, voltage is 415V n full load amps is 805 something,when are applied load more than 400 amps it's voltage is dropping, what is the reasons...?
Answers were Sorted based on User's Feedback
Answer / sanjay
There can be one of the following reason for the problem :
1.The AVR may be faulty.
2.The conductor is of lesser current rating.
3.Loose connection/faulty cable termination
4.Load is quiet far off from generator.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / dharmans
1.mainly in AVR RRA diodes problem or lose termination.
Is This Answer Correct ? | 3 Yes | 0 No |
iT SEEMS THE EXCITATION SYSTEM IS NOT TUNED PROPERLY.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / satya dev
There is a lot of reasons to droping thevoltage during the
load.
Electrical reason - 1. Excitation voltage is not build up
to the requiered limit.
2.Fuel pump actuator is not working properly.its required a
certain DC voltage for certain load.
Mechanical Reason- If the DG set is more than two cylinders
may be one piston is not working properly, may be push rod
of the piston got broken.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the difference between mho characteristics and quadrilateral chara in distance protection
Does voltage and current can be seperated?
while buying 30 kva on line ups for 1 phase ouput, we ave to calculate the number of batteries for 2 hours back up? how to calculate the ah rating and number of batteries
what is recovery voltage & transient voltage ?
what is rise time and half time
why m and c are shorted in wattmeter
After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.
why C.T secondary are rated 5A generally?
what is the charging battery current of 80 kva UPS/100AH bocket make battery.
what is meant by skin effect ?
what is the meaning of number in (11, 31, 61,14, etc. CDG11, CDG31, CDG61, DDT32
IN a transformer during power supply how the LV and HV bushing works??