what is the function of supervison relay?Draw its wiring
diagram.
Answers were Sorted based on User's Feedback
Answer / dnt
The trip circuit extends beyond the relay enclosure and
passes through more components, such as fuses, links, relay
contacts, auxiliary switch contacts and so on, and in some
cases through a considerable amount of circuit wiring with
intermediate terminal boards.
These complications, coupled with the importance of the
circuit, have directed attention to its supervision.The
relay use for supervision called supervision relay.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / mohan
tripping relay supervision is also known as master trip relay
its relay code is 86 its command make the circuit breaker to
release the contacts it is one of the main relays used in electrical circuits
| Is This Answer Correct ? | 2 Yes | 0 No |
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
What is a LBB protection and why it is used?
What is the difference between a 3 winding and 2 winding Potential Transformer
what is merz price protection
Differene between KVA and KW.
What are the relays in ACB and VCB
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
what is suitable cable for 25 HP motor ? start with VFD ac supply 50 hz
what should be the air clearence between phase to phase, phase to earth in Medium voltage switchgear for 3.3kv,6.6kv,11kv,22kv and 33kv? Which is to be referred for this?
y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..
what is the relation between frequency and inductive reactance in a d.c supply?
what is mean impedance?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)