what is merz price protection

Answers were Sorted based on User's Feedback



what is merz price protection..

Answer / nitin lothe

Its the protection scheme used for Power Transformers to
detect internal faults n also termed as Differential
Protection. If there is difference in currents on HV and
corresponding LV side of transformer of the same phase,
protection will operate.

Is This Answer Correct ?    118 Yes 18 No

what is merz price protection..

Answer / shyam kishor

Merz-Price protection is the method used for protection of alternators. it is a most common system used for the protection of stator winding faults employs circulating current principle. in this scheme of protection,current at the two ends of the protected section are compared. under normal operating conditions,these currents are equal but may become unequal on the occurrence of a fault in the protection section. the difference of the currents under fault condition is arranged to pass through the operating coil of the relay. the relay then closes its contacts to isolate protected section from the system.(Ref. book on power system v.k mehta and rohit mehta)

Is This Answer Correct ?    65 Yes 8 No

what is merz price protection..

Answer / sudipt jena

Merz Price is also called Differential protection. And is used to protect alternator and also transmission line.For this we have two engage CT's at both the ends of the portion/equipment to be protected. In this method breaker trips, if fault occurs within both the CT's only, and not for outer zone.

Is This Answer Correct ?    14 Yes 1 No

what is merz price protection..

Answer / satish

This type of protection provides a continuous check on faults within the points, where the C.T.s are used as in shown in fig 2. There are two sets of C.T.s; each set is mounted on either end of the stator phase. The secondaries of these current transformer sets are connected in star and their ends are connected together through pilot wires. The over current inverse time relay is connected across the equipotential points in the pilot wires, which will naturally be in center of these wires as shown in fig 2. But it’s convenient to locate these relays adjacent to the main circuit breaker; this can be achieved by inserting balancing resistance in series with the pilot wires to achieve equipotential point near the main circuit breaker as shown in fig 3. If there is no fault in the generator, same current will pass through the C.T.s at both the ends and there will be no current spilling into the relay.



Now if earth fault occurs as shown in fig 2, there will be an increase in current through set C.T.1 as compared to current through C.T.2. Thus there is no current balance any more resulting into spilling of current through the relay R hence tripping the circuit. If there is short circuit between the two phases as in fig3 it will also cause operation of relay R and tripping of the circuit breaker. This scheme does not provide protection for the turns of same phase

Is This Answer Correct ?    13 Yes 3 No

what is merz price protection..

Answer / vinay

merz pricr protection mean voltage will be balanced under
no fult condition if fult occur it will unbalanced

Is This Answer Correct ?    31 Yes 30 No

Post New Answer

More Electrical Engineering Interview Questions

what is the speed of a turbine in an hydroelectric power station and how many poles does it have...?

1 Answers  


why and how fault current flows through ground?

1 Answers  


can induction motor run over the rated speed ?

12 Answers   ACC,


i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?

0 Answers  


what is the difference between oil surge relay and buchholz relay.

0 Answers   MPPEB, Suparco,






The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is

0 Answers   Caterpillar,


What is VCB? where it is installed at SP. What is SP?

0 Answers  


why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable for slipring induction motor?

5 Answers  


At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of starting it draws 840A instead of 390A (7.2%). As per the data sheet also its 390A starting current. it thru a dol starter from the MCC. can anyone tell what is the problem in the motor

5 Answers   ME,


how to calculate the ac and dc wire losses with calculations plz tell me

3 Answers   Apollo,


One amps in HT is equal to how manys amps in LT

5 Answers  


What are the limiting factor for controlling maximum hot point temperature within a hydrogen and water cooled generator?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)