a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of
0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy
of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag
What is the accuracy ratio? is this ratio acceptable?
Answer / markwilcon
Transmitter=0.005 x 2500 = 12.5
comparison gauge = 0.001 x 3000 = 3
Am i on the right track?
Is This Answer Correct ? | 1 Yes | 0 No |
how to calibate level transmiter ?range -150 to +150.what is the zero and span?
What is voltage regulator?
If I installed wrong directions orifice plate then what showing value d.p transmitter?
what is the Analog signal and what is the Digital signal
if we put any thermocouple on a table in a room without any connection,what temperature should it show.
HI, can anybody give details about GAS TREATMENT PLANT CONSTRUCTION,as INSTRUMENTATION ENGINEER what are the responsibilites.what are the instruments mainly instrumentation engineer will deal with
I was working on calibrating turbidity transmitters endress+hauser at effluent polishing plant.We calibrated using NTU buffers.What happened is that when we immersed the sensor, everytime we raise and lower the sensor gradually, the reading will vary.my question is that is there any specifications on what is the required distance from the bottom of the container with buffer to the face of the sensor?Is it ok to install the sensor in a medium which has turbulence specially if bubbles are present?
What is frequency factor in massflow meter? When using frequency output?
Explain the working of an enraf level gauge.
What are the processes Variables?
how the actually positioner of control valve working? where we gave 3-15psi pressure to I/P converter where it is firstly applied ?- on I/P to positioner then what happen? is control valve operate on 3-15 psi or its bench pressure?
what is transducer?