Sq. root of ma-4/16*max. flow,
0% = 0 mmh2o
25% = 12.5 mmh2o
50% = 35.25 mmh2o
75% = 37.5 mmh2o
100% = 50 mmh2o mmh2o
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / che-daniel cabardo
the formula is Q=k(square root percent of 0%,25% and so on.)
therfore k=10,constant..
for example range is 0 to 50 mmh2o
the span is 50 mmh2o.
Q=10 multiply sq. root of 25%= 50%
from the formula: %(span) + LRV
So:
0% = 0 mmh2o
25%= 25 mmh2o
50%= 35.3 mmh2o
75%= 43.30 mmh2o
100%= 50 mmh2o
Is This Answer Correct ? | 4 Yes | 7 No |
what do you mean by cathodic protection?
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
How many problems can be occurring in solenoid valve? And how it can be rectified?
Can we measure pressure using differential pressure transmitter? If yes then how?
Explain the usage of the PLC system?
Why we are using PLC instand of DCS in ESD System? can u explain any one?
List three types Level Gauges with their working principles
what is function test.
which type of signal used in instrument?
3 Answers Emco, Makson, Sail, TATA,
Describe the concept of Gain Scheduling, as currently found as an option in some controllers.
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,