what is the difference between main meter CT and check
meter CT?and what is the difference between main meter PT
and check meter PT?
Answers were Sorted based on User's Feedback
Answer / k.c.bhanu
In an industry the main meter CT's ( highly insulated as
per High voltage standard)primary windings are connected
directly to HT voltage(11KV/33KV)& secondary winding to the
Trivectometer. the check mteres & its CTs are commonly
installed with LT/ low voltage system of Consumer.
The Main PT (HT side) are designed 11KV/110volts or
33KV/110volts the primary windings are connected to the
High voltage & the secodary windigs out put (110 volts)are
connected to the Trivectometer.
Is This Answer Correct ? | 10 Yes | 1 No |
In case of gen stations both are identical , there is no
difference at all
Is This Answer Correct ? | 2 Yes | 1 No |
what is the temperature rise test? explain in brief.with formula.
I need bhel electrical test pattern & paper
why lightning arrester and other equipment earthing conneting from same earth bar ?
how to synchronize 3 phase slip ring induction motors of different ratings.
what is the opencircuit tes &short circuit test in transformers ,why you need this test, in poen your connecting which votmeter why?
losses in transmission lines ?
what will happen if the frequency supplied is more than the frequency of the instrument...?
How REF protects transformer alone? explain with diagram.
How calculate the MTA in relay?
A current of 2A flows for 10 hour through a 100 ohm resistor. The energy consumed by the resistor is:(a) 0.5 kWh(b) 4 kWh(c) 2 kWh(d) 0.02 kWh
PLC Based Process Automoation Panels?
What are all the points to be checked for a newly re-winded motor before installation