why do we use 4-20mA as o/p and why don't use 0-20mA or 5-
21mA?

Answers were Sorted based on User's Feedback



why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?..

Answer / ahmed eid

Ohm's law voltage = current * resistance
of the standerd voltage in the dcs from 1 to 5 voltge
and the standerd resistance of loop 250 oums
so
V=I*R
the first in the low signal 1 volt
1(v)=I*250(r) =.004 A
.004*1000 = 4 MA
the sacand in the high signal 5 volt
5(v)=I*250(r) = 020 A
.020*250 = 20 MA


Is This Answer Correct ?    19 Yes 0 No

why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?..

Answer / d tilston

Two wire transmitters require some power to work. 0-20 mA
would not provide any power at 0 mA.

Power = current x volts, (usually 24 VDC)
Power = 0.004A x 24VDC
Power = 0.096W

Not much power.

Is This Answer Correct ?    4 Yes 0 No

why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?..

Answer / carl_ellis

Question:
why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?

There are systems that use 0-20mA as an output from a
controller. Those are active', powered outputs, not
signals from 2 wire, loop powered field transmitters. 2
wire, loop powered instruments use about 3.5mA to power the
transmitter's electronics, so 2 wire, loop powered
instruments can never go below 3.5mA without losing the
current needed to power the instrument.

An active analog output from a controller that uses the
controller's power from the controller to drive the current
signal can be a 4-20mA signal or a 0-20mA signal.

People in the process industries use the 4-20mA output
because it is a 'live-zero' that immediately indicates a
broken wire or an open circuit if the loop current falls to
0.0mA. Those using 0-20mA probably have a 0-10Vdc or 0-5Vdc
analog input and want to use the entire span with a 500 ohm
or 250 ohm resistor.

As to why 5-21mA is not used, there are conventions used
that make systems maintainable over time. If every analog
output used oddball ranges or spans, it would be near
impossible to maintain the system over time. Given that
many control systems operate in excess of 10 years, it is
important to use standard analog signals in order to keep
the system maintainable.

The convention is 4-20mA, established by the ISA SP-50
standard in 1967. Deviations are punishable. Be warned.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

How can i copy program (parameter) from mm440 (V.F.D.) by using BOP?

0 Answers  


THE OUTPUT OF A CURRRENT TRANSMITTER OR A PNEUMATIC TRANSMITTER HAS A LIVE ZERO?EXPLAIN

2 Answers  


which type of zones used for boiler? & why ?

0 Answers  


what should be distance from tapping point to inallation place of instruments?

3 Answers   Tasnee Petrochemicals,


if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?

1 Answers  






NSV type probe stands for

0 Answers   Qatar Petroleums,


Q1: Consider part of a control loop, which excludes the transmitter, consisting of a process, a controller and a control valve which may be represented by two dead times of 0.5 min each and three exponential lags of 0.8 min., 1.0 min. and 1.5 min. respectively. We wish to express this system as an overall first order plus dead time (FOPLD) model ie gain, time constant and process dead time. (We will see later that this is often done, to simplify controller tuning). For this exercise, gain is considered to be 1.0. (A) If the transmitter is a flow transmitter whose behaviour can be described by a dead time of 0.2 min. and an exponential lag of 0.5 min. in terms of the overall dead time and overall first order lag how can the system behaviour be approximated ? Overall dead time = Overall time constant = (B) If the transmitter is a temperature transmitter with a temperature sensor in a protecting well whose behaviour can be described by a dead time of 0.7 min. and an exponential lag of 15 min. how can the overall system behaviour be approximated now? Overall dead time = Overall time constant =

0 Answers  


What is seeback effect?

3 Answers  


Why we used cage in control valve?

8 Answers  


Can u tell me the principle of the tc,rtd,level switch,pressure switch ,transmitter(pr flow level temp.),vibration...plz

0 Answers   Adani, SRF,


Tell about your IFFCO plant visit.

0 Answers   L&T,


how many types 0f thermocouples?

6 Answers   HZL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)